You can run a parametric table in TRNEDit. You would have to make the
following modifications to your file:
1. Add a constant definition:
CONSTANTS 1
LU_TMY2 = 35
2. Duplicate the statement 'Assign' for all the locations that you want
to study. For example,
ASSIGN ".\Weather\US-TMY2\US-WI-Madison-14837.tm2" 35
ASSIGN ".\Weather\US-TMY2\US-AK-Anchorage-26451.tm2" 36
ASSIGN ".\Weather\US-TMY2\US-AK-Annette-25308.tm2" 37
3. In your data reader, look for the parameter that sets the 'logical
unit number' of the weather data file. Replace the number with the
constant LU_TMY2. For example, if you are using Type109, it would be the
second parameter.
4. In TRNEdit., go to menu 'Parametrics' --> 'New table'. You will see
that the constant LU_TMY2 is among the list of possible parameters to
change. You have enter the values that you assigned in the statements
ASSIGN; in the above example, you should enter 35, 36 and 37.
5. Run the table.
I am attaching a file based on the example 'Begin'. Please let me know
if you have problems implementing this solution.
Best regards,
Diego
Mohit Singh wrote:
> Hi all,
> I have created a SDHW deck file (.dck). I was wondering if there was a
> way i could run that file for all possible locations TMY2 at once and
> not have to run the file for each location individually.
>
> Thanks alot,
>
--
Diego A. Arias
TRNSYS Coordinator
Solar Energy Laboratory
University of Wisconsin - Madison
1500 Engineering Drive
Madison, WI 53706
-------------- next part --------------
An embedded and charset-unspecified text was scrubbed...
Name: begin.dck
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20070810/f703109b/attachment-0001.txt>
More information about the TRNSYS-users
mailing list