Bertrand,
The building model that you choose to use
depends on the complexity of the building that
you are trying to model. If you have a simple,
single zone building that can be represented as a
single temperature (walls and air at the same
temperature) then you can use Type88. If you have
a multizone building but one in which you can
represent the walls and air of each zone with a
single temperature, then you can use Type660, the
TESS Library multizone version of the Type88
lumped capacitance building. If you have a more
complex building and are concerned about more
accuracy in calculating solar radiation effects,
interior surface temperatures, etc. then you should use Type56.
There are some models of spit system air
conditioners in the TESS HVAC Library so you
would not have to model the evaporator,
condenser, compressor, and valve separately. If
you want to model the refrigeration cycle you can
of course but one of the difficulties of doing so
is that the time constant for changes in the
refrigeration cycle is very short (on the order
of a second) while the time constant of the
building is on the order of 5 to 15 minutes
usually. Often there arises a difficulty in
choosing a time step for your simulation that
results in an accurate model of both the building and the refigeration cycle.
Kind regards,
David
>Dear all'
>i want to model a building in which we have an air conditionner with TRNSYS.
>I don't know the proper component i should use
>for the building: Type 88, 56, 34, 12, ..??
>
>the air conditioner is part of a vapor
>commpresion refrigeration system where the
>evaporator should be in the building. for this,
>could you tell me which components i can use
>for the evaporator, the condenser and the throtlle valve?.
>
>yours,
>
>
>
>
>------------------------
>TCHANCHE FANKAM Bertrand
>
>C/O SUH Christopher
>22 kadmeas-BOTANIKOS
>Athens, GREECE
>mobile:+30 69 42 95 59 52
>
>
>Découvrez une nouvelle façon d'obtenir des
>réponses à toutes vos questions ! Profitez des
>connaissances, des opinions et des expériences
>des internautes sur
><http://fr.rd.yahoo.com/evt=42054/*http://fr.answers.yahoo.com>Yahoo!
>Questions/Réponses.
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 2916 Marketplace Drive - Suite 104
Partner Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
"Providing software solutions for today's energy engineering projects"
****************************************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20070420/ffa2c4e9/attachment-0005.htm>
More information about the TRNSYS-users
mailing list