Hi,

You can think of Type48 as a controller for the simulation with a pv 
module and battery storage. The easiest way to simulate a system with a 
PV module and a battery is to use Type48b (Regulator and inverter/system 
with battery storage/maximum point tracking/ state of charge (SOC) 
monitoring) and Type47c (Batteries/Power as input/Shepherd modified 
Hyman Equation), as they only exchange information regarding power.

 From PV panel to Type48:
- If you are using a maximum power tracker, connect the maximum power 
from the PV panel Type 48's input 1. If you are using a different load 
curve, connect the power output from the PV instead.

 From Loads to Type48:
- If you used Type14 to define your hourly loads, connect it to Type 
48's input 2.

Type48 to Type 47:
- Output 2 (power to or from battery) --> Input 1 (Power to or from battery)

Type47 to Type48:
- Output 2 (fractional state of charge) --> Input 3 (Battery fractional 
state of charge)

These two connections between Type47 and Type48 will make TRNSYS to 
iterate until it reaches a solution.  You may find that you need a short 
time step to reach a converged solutions at each time step. I used 0.25h 
and it seemed to work fine.

I will be glad to hear other solutions. Please let me know if you have 
more questions.
Best regards,

Diego

rym chaker wrote:
> Please I have a problem with a type 94 ; I can't understand how I 
> connect this type with type 48 and type 47
> also I need to know how I connect the Input3 and Input4
> Please if any one have an idea; please contact me
> thank you
>  
> Chaker Rym
>
> ------------------------------------------------------------------------
> Ahhh...imagining that irresistible "new car" smell?
> Check out new cars at Yahoo! Autos. 
> <http://us.rd.yahoo.com/evt=48245/*http://autos.yahoo.com/new_cars.html;_ylc=X3oDMTE1YW1jcXJ2BF9TAzk3MTA3MDc2BHNlYwNtYWlsdGFncwRzbGsDbmV3LWNhcnM-> 
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at engr.wisc.edu
> https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
>   


-- 
Diego A. Arias
TRNSYS Coordinator
Solar Energy Laboratory
University of Wisconsin - Madison
1500 Engineering Drive
Madison, WI 53706



More information about the TRNSYS-users mailing list