[TRNSYS-users] Exterior wall against ground
David Bradley
bradley at tess-inc.com
Fri Apr 13 11:08:32 PDT 2007
Abdullahi,
You are correct that you should integrate with
respect to depth and calcuate the average. There
is no simple way to do that directly in
Type77/501 at the moment. It is an interesting
idea for future versions. As a simple
alternative, you can use the Kasuda depth for the
middle of the below grade section of the wall
although it is not quite as correct.
Cheers,
David
At 12:27 4/13/2007, aa1 at brighton.ac.uk wrote:
>David/Daniel,
>
>My only concern with the use of Kasuda
>correlation (in the form used in type 77 &Type
>501) for vertical surfaces like a basement wall,
>is the fact that these components will only give
>the soil temperature at a single vertical point
>(say depth Z,Z1,Z2
..at any given time). If
>your wall is very deep, say 1-2m deep, what you
>need is probably the average temperature of a
>vertical profile ranging between depth Z1 and Z2.
>
>The way to go about this is to integrate the
>Kasuda expression with respect to depth (Z1 to
>Z2). My question to David is whether this is
>achievable with Type77/501? If not perhaps
>Daniel might want to look at the following
>document on how to integrate the Labs/kasuda correlations.
>
>Labs, K. 1989. Earth Coupling. Passive Cooling.
>J. Cook. Cambridge Massachusetts, The MIT Press: 197-346.
>
>Abdullahi
>
>School of the Environment
>University of Brighton
>Cockcroft Building
>Lewes Rd.
>Brighton
>BN2 4GJ
>
>Tel: +44 01273 643455
>
>-----Original Message-----
>From: David Bradley [mailto:bradley at tess-inc.com]
>Sent: 13 April 2007 17:38
>To: Büchele Daniel (Helbling Beratung +
>Bauplanung); trnsys-users at engr.wisc.edu
>Subject: Re: [TRNSYS-users] Exterior wall against ground
>
>Daniel,
> Arie's response is quite correct.
> Additionally, if you do not want to use the
> annual ambient temperature as your boundary
> wall temperature, you can use the temperature
> of undisturbed ground as calculated by the
> Kasuda correlation from Type77. This makes the
> ground temperature a function of depth and time
> of year. Like with Arie's response, it assumes
> that the ground is an infinite source / sink
> and that energy transferred from the building
> through the wall to the ground does not affect
> the ground temperature in the long term. We
> have written a few basement models recently
> that do account for the change in the ground
> temperature due to energy transfer through the
> wall but they assume four basement walls and a
> floor. If you only have one wall below grade
> then you might be best off using Arie's method
> either with the annual average ground temperature or with Type77.
>Cheers,
> David
>
>
>At 12:48 4/12/2007, Helbling Beratung + Bauplanung wrote:
>
>Content-class: urn:content-classes:message
>Content-Type: multipart/alternative;
> boundary="----_=_NextPart_001_01C77D2A.CB11DF05"
>
>Hello everybody
>
>Can anyone, tell me whats the best way to
>simulate a external wall against the ground.
>How can I define the ground ??
>
>Thanks in advance
>
>Mit freundlichen Grüssen / Kind regards
>
>Daniel Büchele
>Dipl. Ing. Gebäudeklimatik- / Technik
>Projektleiter
>
>Helbling Holding AG
>Hohlstrasse 614
>CH-8048 Zürich
>Telefon +41 44 438 18 64
>Mobile +41 79 641 44 03
>Telefax +41 44 438 18 10
><mailto:daniel.buechele at helbling.ch>mailto:daniel.buechele at helbling.ch
>< http://www.helbling.ch >
>
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
>
>****************************************************************************************
>Thermal Energy System Specialists (TESS), LLC
>David BRADLEY 2916 Marketplace Drive - Suite 104
>Partner Madison, WI 53719
>Phone: (608) 274-2577 USA
>Fax: (608) 278-1475
>E-mail: bradley at tess-inc.com
>Web Pages: http://www.tess-inc.com and http://www.trnsys.com
>
>"Providing software solutions for today's energy engineering projects"
>****************************************************************************************
****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 2916 Marketplace Drive - Suite 104
Partner Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
"Providing software solutions for today's energy engineering projects"
****************************************************************************************