Dear Aristotelis,
The assumption in Type756 is that the indoor and outdoor blowers are
either both ON or both OFF. The Type reads total power draw from the
external data file (based on the flow rate input) and subtracts off the
specified blower power and controller power (parameters) so that it may
report compressor power as an output. Because Type756 does not set the
indoor unit flow rate, you need to include a fan model that does set the
indoor (evaporator) flow rate. If all you care about is the total power
draw, you can set the power draw of the fan model to 0 and use only output
8 of Type756, which would include controller, indoor blower, outdoor
blower, and compressor power).
Kind regards,
David
At 08:06 9/19/2006, Aristotelis Avgelis wrote:
>Dear all,
>
>I 'm using TRNSYS 16 simulation Studio and I sould like to put in my
>building a split unit air condition system (wall-mounted),
>that means that I have an indoor and an outdoor unit. I tried to use
>type 756 but it has only one parameter for the blower
>power draw. Which one is it? I have an outdoor blower and an indoor
>blower. In a sample of TESS (type756.tpf) before the type756,
>they have connected an extra blower. It seems that it's the indoor
>blower. This means that the blower in type756 is the blower
>of the outdoor unit? However, the external file with the efficiency
>data of the manufacturer's device seems to include total power
>in fuction with the indoor air flow rate. I'm a bit confused.
>Is it better to use type 665, although I am interesting only for cooling
>operation?
>
>With regards,
>Aristotelis Avgelis
>
>--
>Avgelis Aristotelis
>Dipl. Mechanical Engineer
>Laboratory of Heat Transfer and
>Environmental Engineering
>Aristotle University Thessaloniki
>Box 483 54124 Thessaloniki, GREECE
>Tel: + 30 2310 996011
>Fax: + 30 2310 996012
>e-mail: aavgelis at aix.meng.auth.gr
>URL: http://aix.meng.auth.gr
>
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 2916 Marketplace Drive - Suite 104
Partner Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
"Providing software solutions for today's energy engineering projects"
****************************************************************************************
More information about the TRNSYS-users
mailing list