[TRNSYS-users] Artificial lighting
hotline
hotline at transsolar.com
Thu Sep 7 00:59:46 PDT 2006
Hi Maurizo,
the confusing part is that there are not only several ways to define it but also different control strategies possible.
You may select the following:
Related floor area: 1 m²
Total heat gain: 100 W/m²
convective part: 10 %
control strategie: Define e.g. an input or schedule when the light is on (e.g. depending on the horizontal radiation outside)
scale: 1*SCHEDULE USE (schedule use defines when the room is used an the light might be on e.g. workday 8 am to 8 pm)
The resulting heat gain is:
"convective resulating heat gain" = "Related floor area" * "Total heat gain" * "convective part" * "control strategie" * "scale"
"radiative resulating heat gain" = "Related floor area" * "Total heat gain" * (1- "convective part") * "control strategie" * "scale"
If "scale" and "control strategie" is set 1 you a thermal load of 100 W for your room.
Sincerely,
Marion Hiller
TRNSYS hotline Team
-----Ursprüngliche Nachricht-----
Von: trnsys-users-bounces at engr.wisc.edu [mailto:trnsys-users-bounces at engr.wisc.edu] Im Auftrag von Maurizio Sorce
Gesendet: Mittwoch, 6. September 2006 13:32
An: trnsys-users at engr.wisc.edu
Betreff: [TRNSYS-users] Artificial lighting
Dear all,
I have a problem with the definition of TRNBUILD internal gain "artificial light".
I don't understand the meaning of the required inputs¶meters.. So if I have, for example, the simple situation of an a incandescent lamp of 100 W in a room of 9 sqm I don't know how I have to set the different fields.
Can anyone give me some advices on how to solve this problem?
Thanks,
Maurizio
--------------------------------------------
Maurizio Sorce
DREAM - Dipartimento di Ricerche Energetiche ed AMbientali
Università degli Studi di Palermo
Viale delle Scienze, Building 9 - I-90128 Palermo
tel. +39 091 236111 / fax +39 091 484425
email: dream at dream.unipa.it