[TRNSYS-users] Problem with type 696b

Jeff Thornton thornton at tess-inc.com
Fri Oct 6 19:22:27 PDT 2006


> I have got some problems with the type 696b :
> - the output called "Dry air flow rate" and the input "Air flow rate"
> are not correlated. The mass balance seems to be wrong.
> - the following outputs are always equal to 0 : "Heating energy",
> "Humidification energy", "Cooling energy", "Sensible cooling energy",
> "Satent cooling energy" and "Reheat energy".

Thanks for the e-mail.  There is indeed a typo in the 696 source code.  It turns out that the 5th output (flow rate) is missing and all the other outputs beyond that are shifted up by one.  If you'd like, I can send you the new source code.  Please let me know.  Otherwise simply replace:

200   OUT(1)=T_OUT
OUT(2)=W_OUT
OUT(3)=RH_OUT*100.
OUT(4)=P_OUT
OUT(5)=QS_H
OUT(6)=QL_H
OUT(7)=QT_C
OUT(8)=QS_C
OUT(9)=QL_C
OUT(10)=Q_REHEAT

with

200   OUT(1)=T_OUT
OUT(2)=W_OUT
OUT(3)=RH_OUT*100.
OUT(4)=FLOW
OUT(5)=P_OUT
OUT(6)=QS_H
OUT(7)=QL_H
OUT(8)=QT_C
OUT(9)=QS_C
OUT(10)=QL_C
OUT(11)=Q_REHEAT

Our sincerest apologies.

Jeff

****************************************************************