[TRNSYS-users] Type 56 - strange window U-value
David Bradley
bradley at tess-inc.com
Thu Oct 12 08:05:57 PDT 2006
Gilles,
If I understand correctly, Type56 calculates the window U-value at each
time step and at each iteration in the simulation. The u-value at any point
in time is dependent upon a complex calculation of window pane
temperatures, gas cavity temperatures, zone temperature, and ambient
temperature. The u-value reported in the WindowLib is at some reference
condition and is for the center of glass. There is a Type56 output (NTYPE
50 among the "surface outputs") available to show what value Type56 is
calculating for the window u-value during the simulation.
Cheers,
David
At 07:55 10/12/2006, Gilles Fraisse wrote:
>dear trnsys users ,
>using TYPE 56, we have some problems with the U value of the window. For
>exemple, I use this window from the german library (window type, library ...) :
>
>Unit System : SI, Name : TRNSYS 15 WINDOW LIB, Desc : Waermeschutzglas,Ar,
>1.3 71/59, Window ID : 2002, Tilt : 90.0
>Glazings : 2, Frame : 11 2.270, Spacer : 1 Class1 2.330 -0.010 0.138,
>Total Height: 1219.2 mm, Total Width : 914.4 mm
>Glass Height: 1079.5 mm, Glass Width : 774.7 mm
>
>
>In the *.bui file , I consider an area of 4.15m² . But which value of U
>(and of area) is really used in the simulation ? I have compared with the
>steady state modelling (constant external temperature - solar radiation
>=0, constant internal heat gain ... ) and I cannot find 1.3 W/m²K , nor
>0.85*1.3 + 0.15*8.17/3.6 (If I consider the frame). And there's no problem
>if I delete the window.
>
>Has anybody carried-out the same steady state checking with one window ?
>
>best regards
>G. Fraisse
>
>
>
>
>
>
>
>
>
>°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°
>LOCIE - groupe DENED (Développement Énergétique Durable)
>Polytech'Savoie - Université de Savoie
>Campus Scientifique Savoie Technolac
>73376 - Le Bourget du Lac Cedex (France)
>Tel. +33 (0)4.79.75.88.95 (Fax : 81.44)
>°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°°
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 2916 Marketplace Drive - Suite 104
Partner Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
"Providing software solutions for today's energy engineering projects"
****************************************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20061012/44d8150f/attachment-0001.htm>
More information about the TRNSYS-users
mailing list