[TRNSYS-users] negative value for solar radiation

David Bradley bradley at tess-inc.com
Wed Nov 22 05:33:45 PST 2006


Martina,
   I believe that the error message is being generated by Type56 and that 
"20orientation" means that the solar radiation on the 20th orientation (or 
perhaps on surface number 20) is going out of bounds. Often times this is 
an indication that there is a problem with the incidence angle of solar 
radiation on that surface. For example, there may be solar radiation on a 
surface when the incidence angle says that there should be none. What I 
would suggest you do is to disconnect that particular solar radiation 
connection between your data reader / weather processor and the building 
model and see if you can get your project to run. That may lead you to the 
cause of the error. If not, then I would suggest that you contact your 
distributor to see if they can find the problem in your simulation. If you 
aren't sure who to contact, please send me your user id number (found in 
the file user16.id) and I can put you in contact with the proper person.
Kind regards,
  David

At 03:19 11/22/2006, Martina Pasini wrote:
>Hi, I'm an Italian student, I'm having some trouble with solar radiation, 
>but the message says "negative value for solar radiation on 20orientation 
>encountered" and I don't know if 20orientation (it is written without 
>space between the two words), is refereed to some orientation in 
>particular... I have filtered all the data about radiation with equation 
>that choose the max value between zero and the radiation... I don't know...
>thanks for your kind attention... I apologise for my English...
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users

****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY                           2916 Marketplace Drive - Suite 104
Partner                                        Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages:  http://www.tess-inc.com     and      http://www.trnsys.com

"Providing software solutions for today's energy engineering projects"
****************************************************************************************





More information about the TRNSYS-users mailing list