Stefan,
   I looked at the Type27 code and it looks as though you can just change 
the value of the variable NMAX from 25 to 30 and recompile the workspace 
that is provided with TRNSYS. If you do not have access to a Fortran 
compiler, then you might be able to use the TESS two dimensional bin sorter 
(Type576) that is in the Utility Library. If that is not an option, then 
you might be able to ask some kind person to recompile the DLL for you with 
the increased limit.
Cheers,
  David


At 02:56 5/2/2006, Stefan de Kool wrote:
>Dear all,
>I want to output a histogram of some data (flows) subdivided into 300 
>classes, but type 27 can only take 24 classes. Is there a way to change 
>this (I have no experience with customizing types in fortran yet)? Or is 
>there another work around?
>Kind regards
>Stefan
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users

****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY                           2916 Marketplace Drive - Suite 104
Partner                                        Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages:  http://www.tess-inc.com     and      http://www.trnsys.com

"Providing software solutions for today's energy engineering projects"
****************************************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20060502/c406f7d4/attachment-0005.htm>


More information about the TRNSYS-users mailing list