[TRNSYS-users] Type 56, components of heat gains
Diego A. Arias
daarias at wisc.edu
Fri Mar 31 08:52:03 PST 2006
Hi Timo,
Sorry for taking so long to answer your question. I needed help from our
building experts. Marion Hiller from Transsolar helped me figure out
how to verify these values.
The best way to know how the building is calculating the transmission
of solar radiation is to back calculate the transmissivity, absorptivity
and reflectivity of the window.
With an equation you can calculate the energy that is hitting the window:
Q_total = I_total_on_facade * Area_window,
where I_total_on_facade is the total radiation on the orientation
corresponding to the window.
If you ask the additional outputs from the building QSOLTR (ntype 12)
and QTSPAS (ntype 74), then you can calculate the values of
transmissivity = QSOLTR / Q_total
absorptivity = (QTSPAS - QSOLTR)/Q_total
reflectivity = ( Q_total - QTSPAS)/Q_total
Then, you can finally compare these values with the data in the window
library corresponding to the specific glassing that you used.
I am attaching a modified version of the SunSpace example. It contains
the results of the above calculations. Let's pick a time so we can
compare: at hour 36, the calculated values are:
transmissivity = 0.34
absorptivity = 0.36
reflectivity = 0.29
Incident_angle = 24°
If you go to TrnBuild, then to the window manager, and finally to the
WinID library, you will see that the properties of the glazing used are:
transmissivity_beam (Tsol)@30° = 0.413 ; transmissivity_hemispherical =
0.354
absorptivity_beam at 30° = Abs1 + Abs2 = 0.123+0.201 = 0.321;
absorptivity_hemispherical = 0.132 + 0.191 = 0.323
(There are two values of absorptivity, one for each of the surfaces of
the glazing).
reflectivity_beam(Rfsol)@30° = 0.262; reflectivity_hemispherical = 0.314
The overall results that you get with the above equations are weighted
averages for the beam and solar radiation.
In addition, you can also ask for ntype903, which is a balance of solar
radiation on a window.
I hope this helps. Please do not hesitate to contact me again if you
have additional questions.
Best regards,
Diego
Timo Sengewald wrote:
>Diego,
>
>thanks for your answer. I already tried QSOLTR but it seems the amount
>delivered is too low and I tried QTSPAS (NType 74) which delivers more
>plausible values (compared with the incidence radiation on the outside
>wall).
>
>The documentation says about QSOLTR:
>
>NTYPE 12: QSOLTR total shortwave solar radiation transmitted through
>external windows of
>zone (but not kept 100 % in zone) [kJ/hr]
>
>Isn't the shortwave radiation the visible part of the solar radiation? That
>would explain the pretty low energy rate.
>
>Best regards,
>Timo
>
>________________________________________________
>Timo Sengewald
>
>BLS Energieplan GmbH
>Elsenstraße 106
>D-12435 Berlin
>Tel.: +49 30 53 32 81-0
>Fax: +49 30 53 32 81-40
>
>
>www.bls-energieplan.de
>
>
>
>
>
>-----Ursprüngliche Nachricht-----
>Von: trnsys-users-bounces at engr.wisc.edu
>[mailto:trnsys-users-bounces at engr.wisc.edu] Im Auftrag von Diego A. Arias
>Gesendet: Freitag, 17. März 2006 23:51
>An: Timo Sengewald
>Cc: trnsys-users at engr.wisc.edu; ausgang at bls-energieplan.de
>Betreff: Re: [TRNSYS-users] Type 56, components of heat gains
>
>
>Dear Timo,
>
>Ntype12 (QSOLTR) gives you the total shortwave solar radiation
>transmitted through external windows for a given zone.
>Best regards,
>
>Diego
>
>
>Timo Sengewald wrote:
>
>
>
>>Hello!
>>
>>Currently I try to estimate the single components the total thermal
>>gain of a room is composed of (observing a single day). Could somebody
>>tell me which NTYPES of type 56 deliver the solar radiation
>>transmitted through the windows?
>>
>>
>>Thanks for your help!
>>
>>
>>Best regards,
>>
>>Timo
>>
>>
>>________________________________________________
>>Timo Sengewald
>>
>>BLS Energieplan GmbH
>>Elsenstraße 106
>>D-12435 Berlin
>>Tel.: +49 30 53 32 81-0
>>Fax: +49 30 53 32 81-40
>>
>>
>>www.bls-energieplan.de
>>
>>
>>-----------------------------------------------------------------------
>>-
>>
>>_______________________________________________
>>TRNSYS-users mailing list
>>TRNSYS-users at engr.wisc.edu
>>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
>>
>>
>>
>>
>
>
>
>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: ModifiedSunSpace.zip
Type: application/x-zip-compressed
Size: 59144 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20060331/34e22281/attachment-0005.bin>
More information about the TRNSYS-users
mailing list