[TRNSYS-users] Convection heat transfer coefficients
Diego A. Arias
daarias at wisc.edu
Tue Mar 28 07:59:48 PST 2006
Dear Elena,
You can find the default values for the calculation of the convection
coefficients in the PROPERTIES section of the .inf file:
* P r o p e r t i e s
*--------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------------
PROPERTIES
DENSITY=0.987 : CAPACITY=1.012 : HVAPOR=2454.0 : SIGMA=2.041e-007 :
RTEMP=293.15
*--- alpha calculation -------------------
KFLOORUP=7.2 : EFLOORUP=0.31 : KFLOORDOWN=3.888 : EFLOORDOWN=0.31
KCEILUP=7.2 : ECEILUP=0.31 : KCEILDOWN=3.888 : ECEILDOWN=0.31
KVERTICAL=5.76 : EVERTICAL=0.3
where the heat transfer coefficient ALPHA is calculated as:
ALPHA_i = K_i /3.6 * abs(T_surface - T_air)^(E_i)
If you want, you can look at the source code of Type56 for the
calculation of the heat transfer coefficients
(\SourceCode\Type56\OpenSouce\Open_TYPE56.for). This is done in the
subroutine CALHTC.
I hope this helps.
Best regards,
Diego
Dascalaki Elena wrote:
> Dear TRNSYS Users
>
> Using TRNSYS16 for the calculation of convection coefficients of the
> internal wall surfaces in a very simple building model, I realized
> that I get different results when I use the "internal calculation"
> facility in the wall typemanager menu and when I use Type 80. Could
> you please explain to me where the difference in the two ways of
> calculation process lies?
> I would also like to know where I could find the reference for the
> values of the default coefficients and exponents that are
> incorporated in TRNSYS16. In the Manuals, the default coefficients
> given in TRNSYS16 electronic user's manual (page 65) and in Vol.6
> (paper verion of the manual for Type 56) the default values seem to be
> slightly different.
>
> Thank you in advance,
> Elena Dascalaki
>
> *********************************************************************************************************
> Dr. Elena Dascalaki
> Building Physicist
> Group Energy Conservation (G.R.E.C.)
> Institute for Environmental Research and Sustainable Development (IERSD)
> National Observatory of Athens (NOA)
> I. Metaxa & Vas. Pavlou, GR 152 36, Penteli, Greece
>
> Tel: +30 210 810 9143
> Fax: +30 210 810 3236
>
> e-mail: edask at meteo.noa.gr <mailto:edask at meteo.noa.gr>
> web site: www.noa.gr <http://www.noa.gr>
>
>------------------------------------------------------------------------
>
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
>
>
--
Diego A. Arias
TRNSYS Coordinator
Solar Energy Laboratory
University of Wisconsin - Madison
1500 Engineering Drive
Madison, WI 53706
More information about the TRNSYS-users
mailing list