[TRNSYS-users] dynamicdata function
David Bradley
bradley at tess-inc.com
Tue Jun 13 09:40:18 PDT 2006
Amandine,
This is a common error. The format of the data file read by DynamicData is:
Values of X3
Values of X2
Values of X1
Data
what you used is:
Values of X1
Values of X2
Values of X3
Data
I think you need to rearrange your call to DynamicData so that it reads
(changes are noted in bold):
X(1) = THW_IN
X(2) = TCW_IN
X(3) = TCHW_T1
CALL DYNAMICDATA(LU_S1,NX,NVAL,NY,X,Y,INFO,*10)
CALL LINKCK('TYPE807','DYNAMICDATA',1,807)
10 IF (ErrorFound()) RETURN 1
FNCAP=Y(1)
FNCOP=Y(2)
Kind regards,
David
At 08:26 6/13/2006, Amandine LE DENN wrote:
>Dear users,
>
>a DynamicData procedure is included in Type107 code and it seems a bit
>different that what's described in Trnsys Programmers guide. In a handmade
>Type, I try to read my own file but DynamicData always give me the wrong
>solution.
>
>the code is the following:
>C GET THE PERFORMANCE DATA FROM THE S1 DATA FILE: FRACTION OF DESIGN
>CHILLED WATER CAPACITY
>C AND FRACTION OF DESIGN COP ARE FUNCTION OF INLET HOT WATER TEMPERATURE,
>INLET COOLING
>C WATER TEMPERATURE AND OUTLET CHILLED WATER TEMPERATURE LEVEL
>
> NVAL=3
> NY=2
> NX(1)=5
> NX(2)=3
> NX(3)=5
> X(1)=TCHW_T1
> X(2)=TCW_IN
> X(3)=THW_IN
> CALL DYNAMICDATA(LU_S1,NX,NVAL,NY,X,Y,INFO,*10)
> CALL LINKCK('TYPE807','DYNAMICDATA',1,807)
>10 IF (ErrorFound()) RETURN 1
> FNCAP=Y(1)
> FNCOP=Y(2)
>
>and data file is (separation = tab):
>
>5.5 6 7 8 9 !Chilled Water Temperature output at previous timestep
>24 29.5 31 !Entering Cooling Water Temperature
>75 80 85 88 95 !Inlet Hot Water Temperature
>0.87671 0.88571 ! Fraction of design capacity and design COP at 5.5 24 75
>0.98630 0.88571 ! Fraction of design capacity and design COP at 5.5 24 80
>y1 y2 ! Fraction of design capacity and design COP at 5.5 24 85
>etc...
>
>
>Can someone detect the problem..?
>
>thank you for your help,
>
>Amandine LE DENN
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 2916 Marketplace Drive - Suite 104
Partner Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
"Providing software solutions for today's energy engineering projects"
****************************************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20060613/1af977cb/attachment-0005.htm>
More information about the TRNSYS-users
mailing list