Amandine,
   This is a common error. The format of the data file read by DynamicData is:
Values of X3
Values of X2
Values of X1
Data
what you used is:
Values of X1
Values of X2
Values of X3
Data
I think you need to rearrange your call to DynamicData so that it reads 
(changes are noted in bold):
         X(1) = THW_IN
         X(2) = TCW_IN
         X(3) = TCHW_T1
         CALL DYNAMICDATA(LU_S1,NX,NVAL,NY,X,Y,INFO,*10)
         CALL LINKCK('TYPE807','DYNAMICDATA',1,807)
10      IF (ErrorFound()) RETURN 1
         FNCAP=Y(1)
         FNCOP=Y(2)
Kind regards,
  David
At 08:26 6/13/2006, Amandine LE DENN wrote:
>Dear users,
>
>a DynamicData procedure is included in Type107 code and it seems a bit 
>different that what's described in Trnsys Programmers guide. In a handmade 
>Type, I try to read my own file but DynamicData always give me the wrong 
>solution.
>
>the code is the following:
>C  GET THE PERFORMANCE DATA FROM THE S1 DATA FILE: FRACTION OF DESIGN 
>CHILLED WATER CAPACITY
>C  AND FRACTION OF DESIGN COP ARE FUNCTION OF INLET HOT WATER TEMPERATURE, 
>INLET COOLING
>C  WATER TEMPERATURE AND OUTLET CHILLED WATER TEMPERATURE LEVEL
>
>   NVAL=3
>   NY=2
>   NX(1)=5
>   NX(2)=3
>   NX(3)=5
>   X(1)=TCHW_T1
>   X(2)=TCW_IN
>   X(3)=THW_IN
>   CALL DYNAMICDATA(LU_S1,NX,NVAL,NY,X,Y,INFO,*10)
>   CALL LINKCK('TYPE807','DYNAMICDATA',1,807)
>10   IF (ErrorFound()) RETURN 1
>   FNCAP=Y(1)
>   FNCOP=Y(2)
>
>and data file is (separation = tab):
>
>5.5 6 7 8 9 !Chilled Water Temperature output at previous timestep
>24 29.5 31   !Entering Cooling Water Temperature
>75 80 85 88 95 !Inlet Hot Water Temperature
>0.87671 0.88571  ! Fraction of design capacity and design COP at    5.5 24 75
>0.98630 0.88571  ! Fraction of design capacity and design COP at    5.5 24 80
>y1  y2    ! Fraction of design capacity and design COP at    5.5 24 85
>etc...
>
>
>Can someone detect the problem..?
>
>thank you for your help,
>
>Amandine LE DENN
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY                           2916 Marketplace Drive - Suite 104
Partner                                        Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages:  http://www.tess-inc.com     and      http://www.trnsys.com
"Providing software solutions for today's energy engineering projects"
****************************************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20060613/1af977cb/attachment-0005.htm>
    
    
More information about the TRNSYS-users
mailing list