Dear Amandine,
There are several options to solve your problem:
1.  You can use one Type55 to sum the output during each month (like you 
are doing now), and then another one in parallel to sum the same output 
for the entire year.
In order to add a line to your summary, you can create a copy of the 
printer Type25 (this will make sure that you print to the same file).  
Set the parameters so it prints at the end of the simulation (8760 
hour), change the logical unit to the same one that the original Type 25 
has, and set parameters 8 and 10 to -1.  Finally,  send the output from 
the second Type55 to this instance of Type25.
2.  You can use type28.  The description of this component says:  
"Type28 can be conveniently used to generate daily, weekly, monthly or 
seasonal summaries of information computed in a simulation.  Its output 
can be displayed either in a boxed format or as a table.
Type 28 integrates its inputs over the time interval of the summary, 
performs user specified arithmetic operations on the integrals, and 
prints the results. This configuration prints results to an external file"
Type28 gives you lots of possibilities, but you will have to read the 
mathematical description in order to use the conventions for the operations.
3.  Finally, I think that the easiest solution is to add the 12 lines of 
your file while you post-process your results in a spreadsheet.
Best regards,
Diego
Amandine LE DENN wrote:
> Dear users,
>  
> I calculate the sum of an output over a period of 1 month, each month, 
> during one year using Type55. Then, "Printer" Type25 produce a file 
> with monthly datas (12 lines).
> I would like to calculate the sum of the same output over a period of 
> 1 year, placing a new Type55 in serie, after the first one, doing the 
> sum of 12 monthly values.
>  
> Do you know:
> - how to set the second Type55 parameters?
> - how to write a file containing the 12 monthly values _and_ 
> total annual value.
>  
> I run an hourly simulation of 8760 hr.
>  
> Thank you for your help,
>  
> Amandine LE DENN
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at engr.wisc.edu
> https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
>   
-- 
Diego A. Arias
TRNSYS Coordinator
Solar Energy Laboratory
University of Wisconsin - Madison
1500 Engineering Drive
Madison, WI 53706
    
    
More information about the TRNSYS-users
mailing list