[TRNSYS-users] Cooling with lake water
Diego A. Arias
daarias at wisc.edu
Fri Apr 21 06:36:20 PDT 2006
Dear Johan,
I do not know of any component that models the behavior of a stratified
pond.
However, you may want to try Type 4, which simulates the performance of
a storage tank subject to thermal stratification. The tank is divided
in N nodes, and energy balance equations are solved for each one of the
nodes.
However, there are a couple of issues to take into account:
- Type 4 was developed having domestic hot water applications in mind,
i.e., the objective is to heat the water and the magnitude of the volume
is very different. Type 4 has 3 operation modes: Mode 1 and 2 have
fixed locations for the source and load streams, and the location of
the load stream in these two modes is at the highest point of the tank
(highest temperature). You could use Mode3, which allows you to specify
the nodes where the load and source streams are located.
- You can use 2 heating elements in Type 4. I think that you could use
them to simulate an energy input from the sun.
Please let me know what you think about this strategy. If you find that
Type4 does not suit your needs, I can help you developing a new component.
Best regards,
Diego
Desmedt Johan wrote:
>
> Dear TRNSYS users,
>
> I'm looking for a type in TRNSYS for simulating a pond or lake with
> water (volume: 600000 m³, depth: 10 m) for cooling purposes. The
> temperature at the bottom of the lake is around 6°C. Is there a type
> available in the TRNSYS library which could could serve for this
> application? A model with stratification possibilities would be nice.
>
> Thanks a lot!!
> Johan Desmedt
>
> ========================================
> Johan Desmedt
> VITO
> Expertisecentrum Energietechnologie
> Boeretang 200
> B-2400 Mol (Belgie)
> tel: +32.14.33.58.41
> fax: +32.14.32.11.85
> email: johan.desmedt at vito.be
> http:\\www.vito.be
> ========================================
>
>
>
> ------------------------------------------------------------------------
> This e-mail, any attachments and the information it contains are
> confidential and meant only for the use of the addressee(s) only.
> Access to this e-mail by anyone other than the addressee(s) is
> unauthorized. If you are not the intended addressee (or responsible
> for delivery of the message to such person), you may not use, copy,
> distribute or deliver to anyone this message (or any part of its
> contents) or take any action in reliance on it. In such case, you
> should destroy this message and notify the sender immediately. If you
> have received this e-mail in error, please notify us immediately by
> e-mail or telephone and delete the e-mail from any computer.
> All reasonable precautions have been taken to ensure no viruses are
> present in this e-mail and its attachments. As our company cannot
> accept responsibility for any loss or damage arising from the use of
> this e-mail or attachments we recommend that you subject these to your
> virus checking procedures prior to use.
> ------------------------------------------------------------------------
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at engr.wisc.edu
> https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
>
More information about the TRNSYS-users
mailing list