[TRNSYS-users] help
David Bradley
bradley at tess-inc.com
Thu Sep 8 05:48:09 PDT 2005
Ana,
If you are interested in calculating the total cooling load of the
Type56 building, you can just look at the Type56 default output called
"QSENS" for each zone. This is the amount of energy that must be added to
or removed from the building in order to maintain the set points that you
specify in TRNBuild by turning on the heating and cooling types in each
zone. If, on the other hand, you are interested in putting an absorption
chiller in the building to meet the building's cooling demand then you are
changing from a control mode called "energy rate control" to a control mode
called "temperature level control." In energy rate control, the building
model calculates how much energy was required to maintain a certain set
temperature. In temperature level control, you have a certain amount of
cooling capacity available in your equipment and you implement thermostats,
ducts, fans, pipes, etc. as necessary to try and keep the building at the
desired temperature. To use Type107 and Type56 in conjunction, you will
need to add zone relative humidity outputs and ventilation stream inputs
(air stream temperature, air change rate, and relative humidity) to each
zone that you are trying to condition with the chiller. You will then need
to implement a combination of controllers (Type2 perhaps), a fan (Type3),
an air to water heat exchanger (Type5 can be used), and Type107 to take air
from the building zones, cool it, and return it to the building.
Kind regards,
david
At 06:55 AM 9/7/2005, apalmero at fe.up.pt wrote:
>Dear users,
> I am using Trnsys 16. I would like to know how I can connect the Type 107
>(absorption chiller) to the Type 56 (Multizone Building) for obtaining the
>total cooling load of the building. What are the outputs of Type 107 and
>inputs
>of Type 56 for obtaining this result?
>
> Can you help me?
> Thank you
>Ana Palmero
>
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 2916 Marketplace Drive - Suite 104
Partner Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
"Providing software solutions for today's energy engineering projects"
****************************************************************************************
More information about the TRNSYS-users
mailing list