Dear Amelie:
I think I have an idea of what is happening. I would recommend looking
at section 2.2.8. of the second part of Volume
'6-MultizoneBuilding.pdf'. Paraphrasing what this section explains:
- u_window = f_frame * u_frame + (1 - f_frame) * u_glass
- u_glass = (A_centr * u_centr + A_edge*u_edge) / (A_cent + A_edge)
- u_edge = c_edge,1 + c_edge,2* u_centr + c_edge,3 * u_centr2
where,
u_window : u-value of the window, taking into account edge effects and
frame effects.
u_glass: u-value of the window, taking into account the edge effects.
u_edge: u-value of the glazing edge of the glass. This value is
calculated by the program WINDOW4.1, and in implemented in the window
library.
u_centr: center of glass u-value
Therefore, the value that you get, 2.1 W/(m².K), does not take into
account the edge effects that Prebid is calculating. I hope this
helps. Please let me know if you have additional questions.
Diego
> We have a problem about the U-value of the windows described
> in Prebid. The value given by TRNSYS simulation does not match with
> the one we calculate ourselves.
>
> For example, on a very basic building with only one window and no
> solar radiation at all, when Ug=1.3 W/(m².K), Uf=23.88 kJ/(h.m².K) and
> area of frame per window x=0.15, we calculate Uw=Ug*(1-x)+Uf/3.6*x=2.1
> W/(m².K), and the u-win value output by Prebid is 1.81 W/(m².K).
>
> Is there an explanation to these results and how can we be sure to
> give Prebid the right value of Uframe in ordert to get the right value
> of u-win (here (2.1 w/(m².K) )?
>
--
Diego A. Arias
TRNSYS Coordinator
Solar Energy Laboratory
University of Wisconsin - Madison