[TRNSYS-users] convergence problem
David BRADLEY
bradley at tess-inc.com
Mon Oct 10 07:34:14 PDT 2005
Caroline,
You should first look at your time step. TRNSYS iterates at each time step to
find a solution to the system and if your equation is such that the air change
rate increases a lot for a small change in room temperature then over an hour
long time step, this translates to a large amount of energy transfer. I'd
consider using a time step no larger than about 5 minutes. If that does not
help, then you can turn to using a Type93 to base your control decision on the
room temperature from one timestep prior to the current one.
Kind regards,
david
Quoting Caroline Hoffmann <HoffmannCaroline at gmx.de>:
> Dear TRNSYS users,
>
> Trying to do something simple, things are getting complicated
> I would like to use the zone temperature of TYPE 56 as an input to define
> via an equation a dependent air change rate (simply spoken as the room is
> getting warmer, airchange rate is increasing).
> Doing this I get the message XXX WERE NOT CONVERGED WITHIN THE SPECIFIED
> TOLERANCE AT TIME. I found in the archive the hint that in the case of
> using the room temperature as an input it is necessary to use a TYPE 2
> controller to achieve convergence. But with this solution as far as I know
> it is just possible to define a threshold value (after which airchange is
> starting) and not a variable airchange rate as I would like to.
> Using trnflow would be a solution, but for this simulation I use a measured
> weather data set, which contains no data of wind speed.
>
> Could anybody give me please a hint how I could solve this problem within
> TRNSYS 15?
>
> Thank you in advance,
>
> Caroline
>
> --
> 10 GB Mailbox, 100 FreeSMS/Monat http://www.gmx.net/de/go/topmail
> +++ GMX - die erste Adresse für Mail, Message, More +++
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at engr.wisc.edu
> https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
>
--
David BRADLEY
Thermal Energy System Specialists, LLC
2916 Marketplace Drive - suite 104
Madison, WI 53719
USA
Ph: +1 608 274 2577
Fax: +1 608 278 1475
Email: bradley at tess-inc.com
More information about the TRNSYS-users
mailing list