[TRNSYS-users] type 16 radiation processor
    Diego A. Arias 
    daarias at wisc.edu
       
    Thu Nov  3 09:27:40 PST 2005
    
    
  
Dear Javier:
I tried using the data from Meteonorm for Madrid using Type89d (TMY2 
standard), and then, connecting it with Type16i.  Changing the time 
shift from -14 to -16 did not make much difference.  When I compared 
with the results from reading the data with Type109, I get the same results.
In the previous email, looked like using a time-shift of -16 you got the 
same results.   I think that the difference at sunrise might be due to 
rounding error when the difference between solar angle and sunrise angle 
is calculated in Type109.
I agree with you that the shift should be -16°.   Zaragoza, Spain: 
Long.= 1°West , LSM=15° East (UTC+1), Shift=-15°-1°= -16°
If you still have problems, I will be happy to help you. Please send me 
the project file and the weather data and I could take a look at it.
Thanks.
Diego
javier mota wrote:
> type 16 radiation processor.
> hallo all;
> i am javier mota from 3i-ingenieria madrid spain
> I have gor a curious result;
> for zaragoza latitude 41.4N;longitude 1.01W , UTC +1.
> so i calculte shift; -15-(1)=-16 and i got that solar constant has 
> been exceed 2 time-steps
> but if i make:-15-(-1)=-14 all data is correct and no warnings.
> I think the correct value is shift -16.
> am I ok?
> must I think there is an error in the data from Institute of 
> meteorology in spain type16 reads, but no in the way type 16 calcula?tes.
> Is correct shift=-16 or -14
> Thank you in advance
>
> _________________________________________________________________
> Horóscopo, tarot, numerología... Escucha lo que te dicen los astros. 
> http://astrocentro.msn.es/
>
> _______________________________________________
> TRNSYS-users mailing list
> TRNSYS-users at engr.wisc.edu
> https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
-- 
Diego A. Arias
TRNSYS Coordinator
Solar Energy Laboratory
University of Wisconsin - Madison
1500 Engineering Drive
Madison, WI 53706
    
    
More information about the TRNSYS-users
mailing list