AW: [TRNSYS-users] active wall transfer functions
hotline
hotline at transsolar.com
Wed Jun 22 01:15:41 PDT 2005
Dear Adriana,
Yes, for the calculation the wall is splitted by TRNBuild into two parts
at the level of the active layer. Otherwise the transfer function method wouldn't work.
However, this "trick" should bother you at all. You can look at it as one wall
as you defined it in TRNBUILD.
Kind regards,
Marion Hiller
Ihr TRNSYS Hotline Team
____________________________________________________ Mailto:Hotline at transsolar.com; http://www.transsolar.com
-----Ursprüngliche Nachricht-----
Von: trnsys-users-bounces at engr.wisc.edu [mailto:trnsys-users-bounces at engr.wisc.edu] Im Auftrag von Adriana Angelotti
Gesendet: Mittwoch, 22. Juni 2005 09:39
An: trnsys-users at engr.wisc.edu
Betreff: [TRNSYS-users] active wall transfer functions
Dear all,
I'm modeling a radiant ceiling as an active wall in type 56.
In the corresponding inf file two transfer functions are generated
for the single active wall, as you can see below.
Beside this, there are also two U values. What does it mean? Is the
active wall split into two parts?
Thank you for any suggestions.
Adriana
---------- WALL TYPE SOFFITTO_RAD_W1 ----------
THERMAL CONDUCTANCE, U= 8.05263 kJ/h m2K; k-Wert= 1.62059 W/m2K
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 3.0911537E+01 4.1459660E-01 3.0911537E+01 1.0000000E+00
1 -3.2298443E+01 2.9786315E+00 -3.2298443E+01 -4.5968926E-01
2 5.9599377E+00 1.0543430E+00 5.9599377E+00 1.4279958E-02
3 -1.0720429E-01 1.8285950E-02 -1.0720429E-01 -6.5467173E-06
4 3.5107225E-05 4.7237405E-06 3.5107225E-05
SUM 4.4658618E+00 4.4658618E+00 4.4658618E+00 5.5458415E-01
---------- WALL TYPE SOFFITTO_RAD_W2 ----------
THERMAL CONDUCTANCE, U= 4.13194 kJ/h m2K; k-Wert= 0.96037 W/m2K
TRANSFERFUNCTION COEFFICIENTS
K A B C D
0 4.5769060E+00 3.8861786E+00 7.4509511E+00 1.0000000E+00
1 -4.4496156E-01 2.4576587E-01 -3.3190067E+00
SUM 4.1319444E+00 4.1319444E+00 4.1319444E+00 1.0000000E+00
---------------------------------------------------
Adriana Angelotti, PhD
Politecnico di Milano
Dipartimento Best
v. Bonardi 3
20133 Milano
Italy
Tel/Fax + 39 02 2399 5118