[TRNSYS-users] Control strategy
David Bradley [SEL]
dbradley at engr.wisc.edu
Tue Jun 21 08:46:48 PDT 2005
Maurizio,
It looks from what you describe as though your best option would be to
write a new controller component. You cannot directly implement the
IF..THEN..ELSE structure using EQUATIONS in an input file.Often times
you can fake an IF..THEN..ELSE statement using one of the Boolean
functions as a multiplier on the variables that you wish to set. For
example, if your condition were:
IF (T_supply_air < T_set_supply - dT_dec) THEN
mode = -1
mode_status = 0
ELSE
mode = 1
mode_status = 0
ENDIF
then you could get the same effect by putting the following in your
input file:
EQUATIONS 3
ModeCheck = LT(T_supply_air,(T_set_supply - dT_dec)) !ModeCheck has a
value of 1 when T_supply_air is less than T_set_supply-dT_dec and 0
otherwise
mode = -1*ModeCheck + 1*(ModeCheck-1)
mode_status = 0
however, the control scheme that you describe below is too complex for
such tricks I think. The other alternative is that you might be able to
implement your control strategy in Type40.
> In addition, does exist a manual for the equation tool?
>
The Simulation Studio equation tool is described in section 2.7 of the
Simulation Studio manual (volume 2 of the TRNSYS 16 documentation set).
There is additional information about the functions that can be
implemented in equations in section 7.6.8 of the 07-TRNEdit manual.
Kind regards,
David
--
David BRADLEY
TRNSYS Engineer
Solar Energy Laboratory - University of Wisconsin, Madison
1500 Engineering Drive
Madison, WI 53706
United States
ph: +1 608 263 1589
fax: +1 608 262 8464
email: dbradley at engr.wisc.edu