[TRNSYS-users] ligts in office

Denis Bourgeois denis.bourgeois at arc.ulaval.ca
Thu Feb 3 05:21:57 PST 2005


MessaggioPietro,

A few weeks ago, I suggested the following documentation (on another forum, me thinks):

Abushakra B., Sreshthaputra A., Haberl J. and Claridge D.E. (2001) "Compilation of diversity factors and schedules for energy and cooling load calculations" American Society of Heating, Refrigerating and Air-conditioning Engineers RP-1093.

Claridge D.E., Abushakra B., Haberl J. and Sreshthaputra A. (2004) "Electricity Diversity Profiles for Energy Simulation of Office Buildings" ASHRAE Transactions 110(1).

Beware: lighting diversity profiles suggested by ASHRAE-RP-1093 apply to core zones, not peripheral zones subjected to natural illuminance ...

Lighting power densities of 10-15 W/m² make sense in open-plan office areas; 15-20 W/m² would likely apply to cellular offices ...

Hope this helps,

Denis Bourgeois
École d'architecture, Université Laval
(418) 686-0695 ou
(418) 656-2131, poste 7489 (local 1206)
denis.bourgeois at arc.ulaval.ca
  ----- Original Message ----- 
  From: Pietro Filippi 
  To: trnsys-users at engr.wisc.edu 
  Sent: Thursday, February 03, 2005 6:55 AM
  Subject: [TRNSYS-users] ligts in office


  Hi to all!
  I urgently need (people always do messy works...) internal gains for lights in a public office. I suppose fluorescent types are normally used. I imagined something like 10W/m2 with 40% convective power. Is it reasonable?
  If somebody then has some article or links as Hilde and Denis sent about gains from PC and monitors (many thanks to you a-"gain"...ah,ah...) it would be the best...
  best regards
  Pietro

  Ing. Pietro Filippi
  Nier Ingegneria SpA
  www.niering.it
  Via Altabella 3, 40126 Bologna
  tel: +39 051234359
  fax: +39 051239530



------------------------------------------------------------------------------


  _______________________________________________
  TRNSYS-users mailing list
  TRNSYS-users at engr.wisc.edu
  https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20050203/4c22b998/attachment-0005.htm>


More information about the TRNSYS-users mailing list