[TRNSYS-users] ts15-type 56 effect of wind on heating load
Arie Kalkman
a.kalkman at chri.nl
Mon Aug 29 03:05:59 PDT 2005
Hi Xavier,
The most import wind effect is the dependence of infiltration on wind
pressure. It can be approximated using a polynomial function like a+b*
windspeed+..
A more accurate solution is the calculation of the Cp factor of each
surface, depending on building hight, building shape, roughness of the
surroundings etc., and use the modified Type 56 in TRNSFLOW
The heat transfer coefficient of the outer surfaces is also dependent on
wind speed, but for well isolated buildings this can usually be negelected.
regards, Arie.
-----Oorspronkelijk bericht-----
Van: Xavier Dequaire [SMTP:xavdeq at futurich.com]
Verzonden: maandag 29 augustus 2005 10:54
Aan: TRNSYS-users at engr.wisc.edu
Onderwerp: [TRNSYS-users] ts15-type 56 effect of wind on heating load
Hi,
type 56 does not take wind as an input,
Any method to simulate the effects of wind on the energy consumption of
the building?
thank you
Xavier D.
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users at engr.wisc.edu
https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
More information about the TRNSYS-users
mailing list