[TRNSYS-users] fixed shading
David Bradley
bradley at tess-inc.com
Thu Apr 21 13:46:38 PDT 2005
Christophe,
The most complete way to treat shaded windows in Type56 is to define a
new orientation for each of the windows and each of the walls that you want
to treat differently. For example, if you have a south facing wall and two
windows in that wall that are shaded by different awnings then you should
define three ORIENTATIONS in TRNBuild. When it comes time to define the
windows themselves, you add them under the "Additional Windows" category at
the zone level instead of adding them to the wall in which they are
contained. You should keep in mind that you need to enter the net wall area
(wall area minus window area) for the south wall because TRNBuild no longer
knows that there are windows associated with that wall. When you generate
the Type56 files, you will be asked for three different total radiations,
three different beam radiations, and three different incidence angles. You
then hook up the outputs of your weather reader / radiation processor and
Type34 to the appropriate Type56 inputs.
Kind regards,
David
At 09:35 AM 4/20/2005, Enertech wrote:
>Dear TRNSYS Users,
>
>I would like to define 2 different windows with 2 different fixed shading
>in a same external wall. I think to use 2 type34, to sum the outputs :
>- Incident receiver radiation = Incident receiver radiation 1 +
>Incident receiver radiation 2
>- Beam radiation on receiver = Beam radiation on receiver 1 + Beam
>radiation on receiver 2
>And to connect these sums to the TYPE 56 inputs ITSHAD and IBSHAD
>respectively. Do I thinking right ? If I don't, what's the solution ?
>
>Thanks.
>
>Christophe Plantier
>===========================
>ENERTECH
>F-26160 FELINES SUR RIMANDOULE
>tel-fax : 04 75 90 18 54
>Email : sidler at club-internet.fr
>Web : http://perso.club-internet.fr/sidler
>================================
>_______________________________________________
>TRNSYS-users mailing list
>TRNSYS-users at engr.wisc.edu
>https://www.cae.wisc.edu/mailman/listinfo/trnsys-users
****************************************************************************************
Thermal Energy System Specialists (TESS), LLC
David BRADLEY 2916 Marketplace Drive - Suite 104
Partner Madison, WI 53719
Phone: (608) 274-2577 USA
Fax: (608) 278-1475
E-mail: bradley at tess-inc.com
Web Pages: http://www.tess-inc.com and http://www.trnsys.com
"Providing software solutions for today's energy engineering projects"
****************************************************************************************
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/attachments/20050421/3b390514/attachment-0001.htm>
More information about the TRNSYS-users
mailing list