Olympia,
> 
>  I am working on the TRNSYS simulation of a six-floor building.
>  I have used the type *type56w_outfiles*.
> After simulation I get 3   .plt files. One of them is the monthly symmary
> 
> Can someone explain me the exactly meaning of SOLAR_RAD
> (Is it a total of shortwave solar radiation transmitted through windows,
> radiation transmitted through the envelope etc?)
My understanding is that SOLAR_RAD in the automatic monthly summary is 
Output NTYPE = 12:
QSOLTR, shortwave (solar) radiation transmitted through all external 
windows in the zone (but not kept 100% in the zone).
This gives you an idea of the solar gains in your zone, but you have to 
be careful if you want to use that output in energy balances (because of 
the "not kept 100% in the zone")
The good news is that TRNSYS 16 comes with additional automatic output 
files with more energy balances than you will ever need, which will 
spare you that kind of problems.
Kind regards,
Michaël Kummert
-- 