[TRNSYS-users] Type 56w_outfiles

Michaël Kummert kummert at engr.wisc.edu
Fri Nov 5 07:39:32 PST 2004


Olympia,
> 
>  I am working on the TRNSYS simulation of a six-floor building.
>  I have used the type *type56w_outfiles*.
> After simulation I get 3   .plt files. One of them is the monthly symmary
> 
> Can someone explain me the exactly meaning of SOLAR_RAD
> (Is it a total of shortwave solar radiation transmitted through windows,
> radiation transmitted through the envelope etc?)

My understanding is that SOLAR_RAD in the automatic monthly summary is 
Output NTYPE = 12:
QSOLTR, shortwave (solar) radiation transmitted through all external 
windows in the zone (but not kept 100% in the zone).

This gives you an idea of the solar gains in your zone, but you have to 
be careful if you want to use that output in energy balances (because of 
the "not kept 100% in the zone")

The good news is that TRNSYS 16 comes with additional automatic output 
files with more energy balances than you will ever need, which will 
spare you that kind of problems.

Kind regards,

Michaël Kummert

-- 
_________________________________________________________

Michaël Kummert

Solar Energy Laboratory - University of Wisconsin-Madison
1303 Engr Res Bldg, 1500 Engineering Drive
Madison, WI 53706

Tel: +1 (608) 263-1589
Fax: +1 (608) 262-8464
E-mail: kummert at engr.wisc.edu

SEL Web Site: http://sel.me.wisc.edu
TRNSYS Web Site: http://sel.me.wisc.edu/trnsys



More information about the TRNSYS-users mailing list