[TRNSYS-users] Type 60d Error
Michaël Kummert
kummert at engr.wisc.edu
Mon Dec 6 09:06:52 PST 2004
Sigrid,
> I have modeled a simple combisystem with a type 60d including two submersed heat exchangers, 1 inlet and 1 outlet.
> I can not run the simulation a whole year, I get the following error:
> %%% TYPE60 WARNING: UAhx UNABLE TO
> CONVERGE IN 500 ITERATIONS AT TIME=
> 18.00000 500 %%%
> 18.00000 B 1569.571
> Nevertheless if I run the simulation for each month there is no problem.
This is a known issue in Type 60, which has been addressed in TRNSYS 16.
Usually it is possible to alleviate the problems by reducing the time
step. The problem is also often linked to using glycoled water in the
heat exchanger. It is possible to use pure water and "cheat on the
flowrate" to obtain the same capacitance flowrate.
The fact that you can run the simulation one month at a time probably
comes from the "warnings" limit. You can increase it in your input file
and then you should be able to run the file for a whole year. You should
be especially careful and check that the results make sense, though.
Sometimes the non-convergences in the heat excahgner happen at very low
flowrate so they don't have a real effect on the simulated performance
but in some circumstances such problems can lead to important errors in
the heat exchanger energy balance.
So my recommendataions are: try to reduce the time step, calculate and
check the heat exhanger energy balance in your simulation and increase
the maximum number of warnings. Also possibly use pure water with a
modified flowrate if you were using glycol.
Or give a try to TRNSYS 16!
Kind regards,
Michaël Kummert
--
_________________________________________________________
Michaël Kummert
Solar Energy Laboratory - University of Wisconsin-Madison
1303 Engr Res Bldg, 1500 Engineering Drive
Madison, WI 53706
Tel: +1 (608) 263-1589
Fax: +1 (608) 262-8464
E-mail: kummert at engr.wisc.edu
SEL Web Site: http://sel.me.wisc.edu
TRNSYS Web Site: http://sel.me.wisc.edu/trnsys
More information about the TRNSYS-users
mailing list