[Trace-users] Campus Distribution Losses (UNCLASSIFIED)
Eurek, John S CIV USARMY CENWO (US) via Trace-users
trace-users at lists.onebuilding.org
Mon Feb 13 12:23:40 PST 2017
CLASSIFICATION: UNCLASSIFIED
Where in the climate-change am I supposed to input the 5% and 10% distribution losses to make the 'reviewer' happy?
Thermal distribution losses - the following values may be used to account for seasonal thermal distribution losses including minor leaks and/or condensate losses (but not pumping energy, which must be accounted for separately where it applies):
- chilled water district cooling 5%
- hot water district heating 10%
- closed loop steam systems 15%; open loop steam systems 25%
- steam systems that are partially open/closed must prorate between the above 15% and 25% losses in accordance with the fraction of expected or actual condensate loss
CLASSIFICATION: UNCLASSIFIED
CLASSIFICATION: UNCLASSIFIED