[Trace-users] Ventilation VAV
Oscar Buchely
obuchely at ses-ingenieria.com
Fri May 15 13:30:16 PDT 2015
Thanks for your help. I change the system option in the baseline to Sum Room OA Reqs. I got the same cfm in the baseline and proposed.
On 07/05/2015 04:20 p.m., Keith Swartz wrote:
>
> Oscar,
>
> You can override the baseline ventilation to match the proposed. In
> the “Options” tab of “Create Systems” click on the “Advanced Options”
> in the upper right.
>
> The “System-Level Ventilation Overrides” section is in the lower
> right. Unfortunately the entry is not cfm but % of peak design fan
> airflow.
>
> Keith Swartz, PE
>
> Senior Energy Engineer | *Seventhwave *| *Madison.Chicago.Minneapolis*
>
> (formerly Energy Center of Wisconsin)
>
> 608.210.7123 | www.seventhwave.org <http://www.seventhwave.org/>
>
> *From:*Trace-users [mailto:trace-users-bounces at lists.onebuilding.org]
> *On Behalf Of *Bob Fassbender
> *Sent:* Thursday, May 07, 2015 4:13 PM
> *To:* Oscar Buchely
> *Cc:* trace-users at lists.onebuilding.org
> *Subject:* Re: [Trace-users] Ventilation VAV
>
> Hi Oscar,
>
> If you followed the manual for BOTH the proposed and baseline and
> implemented the same std 62.1 parameters in both, ironically, that's
> what should happen i. The critical ventilation changes as a result of
> the alterations in the baseline's envelope and internal loads. This of
> course impacts the total system ventilation.
>
> Most likely, you want to 1) ensure that your proposed ventilation
> matches the design ventilation (which should match with std 62)
>
> 2) set room by room ventilation in the baseline to match exactly with
> the room ventilations of the proposed. I am pretty sure TRACE does
> this when you select "New ASHRAE 90.1 baseline"
>
> Of course, I'm just guessing on your baseline setup,
>
> Cheers,
>
> Bob
> Energy-models.com
>
> ᐧ
>
> On Thu, May 7, 2015 at 2:52 PM, Oscar Buchely
> <obuchely at ses-ingenieria.com <mailto:obuchely at ses-ingenieria.com>> wrote:
>
> Hi.
>
> I am modelling a VAV systems in base line and proposed models for
> LEED certification purpose. Even though I followed the Trace 700
> user manual steps for introducing 62.1 air flows I don't get the
> same Nom Vent in the system check sums report for the baseline
> and proposed system?.
>
> Thanks
>
> --
>
> _______________________________________________
> Trace-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> TRACE-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:TRACE-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20150515/2ee7fdaa/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 43732 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20150515/2ee7fdaa/attachment-0004.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 62537 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20150515/2ee7fdaa/attachment-0005.jpeg>
More information about the Trace-users
mailing list