[Trace-users] Control Panel & Interlocks

Oscar Buchely obuchely at ses-ingenieria.com
Mon Aug 25 06:41:10 PDT 2014


Hello Mike

I had the same problem. The reviewer asked me why I got electric 
consumption for a gas boiler. In the reply I explained him about the 
interlock component and it was fine.
After that question I always  deleted the interlock component so I don´t 
get any comments on that. I don´t think is a good idea to put them as 
process load because its part of the hot water system.

On 22/08/2014 05:00 p.m., Mike Oliva wrote:
> I'm modeling for LEED and trying to make sure I have everything 
> accounted for w/ in the requirements and for submitting to LEED online 
> but I think I have an issue with the way TRACE applies these energy 
> riders of the control panel & interlocks to some plants (90.1 boiler = 
> 0.5kw).  For one, the energy use is applied to electrical space 
> heating component even if Gas (ex. boiler) and LEED does not allow 
> electrical space heating use for fossil fuel heating source, so I 
> extract that energy use to define as process energy. I have a boiler 
> in both cases so both are modeled with the same rider (0.5kw).
>
> The next issue I come up w/ since I've pulled out that electrical as 
> process is that the proposed boiler runs for much fewer hours than the 
> baseline so even tho the control panel interlock energy use is the 
> same for each, the difference in run time causes the baseline to be 
> quite a bit more.
>
> Curious what folks are doing in this situation, or has it ever come 
> up?  are you creating copies of all the Trace 90.1 plants and removing 
> the control panel & interlock component?
>
> Thanks,
> Mike
>
>
> _______________________________________________
> Trace-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to TRACE-USERS-UNSUBSCRIBE at ONEBUILDING.ORG