[Trace-users] GSHPs in Trace 700
Dahlstrom, Aaron
ADahlstrom at in-posse.com
Mon Sep 23 11:21:18 PDT 2013
Joe -
The information I have heard (from this list serv, help files, and Trane Trace) has indicated that Trace can only model one geothermal plant per TRC file.
That said, I see nothing that would prohibit you from setting up multiple systems that all reference a common plant.
However, there will be a single "compressor" modeled.
Not sure if this is a LEED model - if so, per a recent LEED review we received, GBCI has requested us to -either- use the minimum EER / COP of all relevant heat pumps as the EER/COP entered into Trace, or to conduct averaging based on the ton-hours (eg capacity, quantity, hours of operation) of each system.
Aaron
Aaron Dahlstrom, PE, LEED(r) AP
In Posse - A subsidiary of AKF| 1500 Walnut Street, Suite 1414, Philadelphia, PA 19102
d: 215-282-6753| m: 267-507-5470| In Posse: 215-282-6800| AKF: 212-354-5656
e: ADahlstrom at in-posse.com | in posse web: www.in-posse.com<http://www.in-posse.com/> | akf web: www.AKFGroup.com
From: trace-users-bounces at lists.onebuilding.org [mailto:trace-users-bounces at lists.onebuilding.org] On Behalf Of Joe Chappell
Sent: Monday, September 23, 2013 2:06 PM
To: 'trace-users at lists.onebuilding.org'
Subject: [Trace-users] GSHPs in Trace 700
Hello,
I am currently attempting to model several ground source heat pump systems on a single ground loop all in the same cooling plant. Two of the ground source heat pumps have energy recovery and two do not. In my analysis reports I am only seeing energy usage in "Cooling Equipment - Cooling Mode" for one of the four heat pumps. Is Trace able to model this arrangement? Any tips on how to handle would be greatly appreciated.
Joe
This e-mail may contain information that is confidential, privileged or otherwise protected from disclosure. If you are not an intended recipient of this e-mail, do not duplicate or redistribute it by any means. Please delete it and any attachments and notify the sender that you have received it in error. Unintended recipients are prohibited from taking action on the basis of information in this e-mail. E-mail messages may contain computer viruses or other defects, may not be accurately replicated on other systems, or may be intercepted, deleted or interfered without the knowledge of the sender or the intended recipient. If you are not comfortable with the risks associated with e-mail messages, you may decide not to use e-mail to communicate with In Posse.