[Trace-users] Split System with DOAS for LEED (UNCLASSIFIED)

Robert Arnott arnott.robert at gmail.com
Fri Feb 4 11:59:25 PST 2011


Hi Doug, John, Anne, Bob, Scott,

Thank you all for your help - all your replies have helped me to carry on
with the model, I'll probably be back here with more questions once I've
progressed further. It's good to know that there's such a helpful community!

Regards,
Robert


On Fri, Feb 4, 2011 at 6:24 PM, Eurek, John S NWO <
John.S.Eurek at usace.army.mil> wrote:

> Classification: UNCLASSIFIED
> Caveats: NONE
>
> Bob(s)
>
> Mr. Fassbender, Your answer confuses me.
>
> You say it is not acceptable to model as 1 system, but the image you
> attached shows that you are using the "dedicated OA" tab.
>
> The second concern I have is that my outside air unit has energy recovery,
> but the fan coils do not.  Like Mr. Arnott's system, the heating and
> cooling
> unit is return only with no outside air.  So if I make a fan coil system,
> then input the information under the 'dedicated OA' tab, if I input my
> energy recovery under with 'options' tab will Trace know to credit the
> energy recovery to the DOA unit, because the fan coil has no energy
> recovey.
>
> Mr. Fassbender, can you explain what you meant by not modeling with 1
> system?
>
> Also, I need to look deeper into the exhaust situation, thanks for the tip
> before I even needed it.
>
>
> John Eurek PE, LEED AP
> Mechanical Engineer,
> US Army Corps of Engineers
> Omaha District CENWO-ED-DA
> 1616 Capitol Avenue
> Omaha, NE 68102
> Phone: (402) 995-2134
> email: john.s.eurek at usace.army.mil
>
>
>
> -----Original Message-----
> From: Bob Fassbender [mailto:bob at energy-models.com]
> Sent: Thursday, February 03, 2011 4:30 PM
> To: Robert Arnott; Eurek, John S NWO
> Cc: trace-users at lists.onebuilding.org
> Subject: Re: [Trace-users] Split System with DOAS for LEED
>
> Robert-
>
> Sorry, but no, it is not acceptable to model as 1 system since your model
> will not match your design documents, and your LEED reviewer will probably
> have a system overload and die. You do not want that blood on your hands.
>
>
> They are both very common points of confusion in TRACE (as John confirms!)
> so I answered your questions at:
>
> http://energy-models.com/forum/energy-modeling-software/trace-700/dedicated-
> oa-and-split-system#comment-1261
>
>
> I posted an image too, and the post is pretty long, so I left it on the
> forum.
>
>
> I briefly addressed John's return air volume problem as well. Don't forget
> to click the image to enlarge it!,
>
>
> Bob
>
> On Thu, Feb 3, 2011 at 3:46 AM, Robert Arnott <arnott.robert at gmail.com>
> wrote:
>
>
>        Hi all,
>
>        I am a new Trace 700 user and I'm busy modelling a building for
> LEED. I'm struggling with two fundamental aspects of how the HVAC system
> modelling works in Trace.
>
>
>        1. The building uses a split unit heating/cooling system, with a
> completely separate dedicated outdoor air system for fresh air. The fresh
> air supply is constant and does not vary with the heating and cooling load.
> The split unit draws air directly from each zone (recirculating indoor air
> only) and is not at all connected to the supply ducting of the fresh air.
> Since there are two completely independent systems serving the same zones,
> how should this be modelled for LEED? Would it be acceptable to assume that
> a single system is being used, and that the heating/cooling is done
> directly
> on the supply air?
>
>        2. All zones receive fresh air, with only the bathrooms exhausting
> air, creating a definite airflow network between the zones. If I set every
> zone's "Adjacent air transfer from room" to the passageway connecting all
> the zones, will Trace determine the correct airflow rate and direction
> between each zone? Or is the adjacent air transfer directional, so that the
> bathroom would need to be set to have an airflow transfer from the passage,
> then the passage would need an airflow transfer from multiple zones (but
> trace only allows a single zone to be set)?
>
>
>        I'd appreciate any feedback. Thanks in advance!
>
>        Regards,
>        Robert
>
>
>         _______________________________________________
>        Trace-users mailing list
>
> http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org
>        To unsubscribe from this mailing list send  a blank message to
> TRACE-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
>
>
> Classification: UNCLASSIFIED
> Caveats: NONE
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20110204/286e360f/attachment-0002.htm>


More information about the Trace-users mailing list