Mr. Fassbender, Your answer confuses me.<br>
<br>
You say it is not acceptable to model as 1 system, but the image you<br>
attached shows that you are using the "dedicated OA" tab.<br>
<br>
The second concern I have is that my outside air unit has energy recovery,<br>
but the fan coils do not. Like Mr. Arnott's system, the heating and cooling<br>
unit is return only with no outside air. So if I make a fan coil system,<br>
then input the information under the 'dedicated OA' tab, if I input my<br>
energy recovery under with 'options' tab will Trace know to credit the<br>
energy recovery to the DOA unit, because the fan coil has no energy recovey.<br>
<br>
Mr. Fassbender, can you explain what you meant by not modeling with 1<br>
system?<br>
<br>
Also, I need to look deeper into the exhaust situation, thanks for the tip<br>
before I even needed it.<br>
<div class="im"><br>
<br>
John Eurek PE, LEED AP<br>
Mechanical Engineer,<br>
US Army Corps of Engineers<br>
Omaha District CENWO-ED-DA<br>
1616 Capitol Avenue<br>
Omaha, NE 68102<br>
Phone: (402) 995-2134<br>
email: <a href="mailto:john.s.eurek@usace.army.mil">john.s.eurek@usace.army.mil</a><br>
<br>
<br>
<br>
-----Original Message-----<br>
</div><div class="im">From: Bob Fassbender [mailto:<a href="mailto:bob@energy-models.com">bob@energy-models.com</a>]<br>
Sent: Thursday, February 03, 2011 4:30 PM<br>
To: Robert Arnott; Eurek, John S NWO<br>
Cc: <a href="mailto:trace-users@lists.onebuilding.org">trace-users@lists.onebuilding.org</a><br>
Subject: Re: [Trace-users] Split System with DOAS for LEED<br>
<br>
</div>Robert-<br>
<br>
Sorry, but no, it is not acceptable to model as 1 system since your model<br>
will not match your design documents, and your LEED reviewer will probably<br>
have a system overload and die. You do not want that blood on your hands.<br>
<br>
<br>
They are both very common points of confusion in TRACE (as John confirms!)<br>
so I answered your questions at:<br>
<a href="http://energy-models.com/forum/energy-modeling-software/trace-700/dedicated-
oa-and-split-system#comment-1261" target="_blank">http://energy-models.com/forum/energy-modeling-software/trace-700/dedicated-<br>
oa-and-split-system#comment-1261</a><br>
<br>
<br>
I posted an image too, and the post is pretty long, so I left it on the<br>
forum.<br>
<br>
<br>
I briefly addressed John's return air volume problem as well. Don't forget<br>
to click the image to enlarge it!,<br>
<br>
<br>
Bob<br>
<br>
On Thu, Feb 3, 2011 at 3:46 AM, Robert Arnott <<a href="mailto:arnott.robert@gmail.com">arnott.robert@gmail.com</a>><br>
wrote:<br>
<div class="im"><br>
<br>
Hi all,<br>
<br>
I am a new Trace 700 user and I'm busy modelling a building for<br>
LEED. I'm struggling with two fundamental aspects of how the HVAC system<br>
modelling works in Trace.<br>
<br>
<br>
1. The building uses a split unit heating/cooling system, with a<br>
completely separate dedicated outdoor air system for fresh air. The fresh<br>
air supply is constant and does not vary with the heating and cooling load.<br>
The split unit draws air directly from each zone (recirculating indoor air<br>
only) and is not at all connected to the supply ducting of the fresh air.<br>
Since there are two completely independent systems serving the same zones,<br>
how should this be modelled for LEED? Would it be acceptable to assume that<br>
a single system is being used, and that the heating/cooling is done directly<br>
on the supply air?<br>
<br>
2. All zones receive fresh air, with only the bathrooms exhausting<br>
air, creating a definite airflow network between the zones. If I set every<br>
zone's "Adjacent air transfer from room" to the passageway connecting all<br>
the zones, will Trace determine the correct airflow rate and direction<br>
between each zone? Or is the adjacent air transfer directional, so that the<br>
bathroom would need to be set to have an airflow transfer from the passage,<br>
then the passage would need an airflow transfer from multiple zones (but<br>
trace only allows a single zone to be set)?<br>
<br>
<br>
I'd appreciate any feedback. Thanks in advance!<br>
<br>
Regards,<br>
Robert<br>
<br>
<br>
</div><div class="im"> _______________________________________________<br>
Trace-users mailing list<br>
<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/trace-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to<br>
<a href="mailto:TRACE-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">TRACE-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br>
<br>
<br>
<br>
<br>
</div>Classification: UNCLASSIFIED<br>
Caveats: NONE<br>
<br>
<br>
</blockquote></div><br></div>