[Trace-users] Demand Controlled Ventilation
Julia Beabout
juliabeabout at yahoo.com
Tue Aug 31 06:14:39 PDT 2010
Hi Richard,
Thanks for the feedback. I think we're really saying the same thing, though.
Critical spaces can throw the calc off - which was the point I was trying to
make as well (i.e. my judgment comment) - but you stated it much more clearly.
Thank you. I was just trying to relay my personal experience that it can
sometimes take more time and work to finagle the critical spaces in Trace than
to do the calcs "by hand" (i.e. spreadsheets) and force them in Trace. I
probably should have qualified my statement by saying that I work on a lot of
labs and healthcare projects which also contain a lot of 100% exhausted spaces
which, again, in my experience, can make the ASH 62 calc even more challenging
and time consuming to manipulate within Trace.
Again, which ever way works for people. I use both approaches depending on the
project. Both are valid as long as one understands the ASHRAE 62 and DCV calc
procedures and what Trace has modeled for OA. I was just attempting to relay my
experience and a possible alternative approach.
Julia
________________________________
From: Richard Ellison <REllison at southlandind.com>
To: Julia Beabout <juliabeabout at yahoo.com>; Jen Redington
<redington at vitetta.com>; trace-users at lists.onebuilding.org
Sent: Tue, August 31, 2010 8:25:26 AM
Subject: RE: [Trace-users] Demand Controlled Ventilation
Jen, Julia,
I’m sorry but I strongly disagree with this e-mail. One must read and
understand ASHRAE 62.1 first to understand how to use Trace for that
calculation. Trace will work properly but you need to know the procedure.
There is some trial and error but it still is as fast as or faster than manually
performing all the ASHRAE 62.1 calculations. Critical rooms may require some
manual adjustment or features like setting the max Z factor can be very
helpful. There is a PDF on the Trane web site I strongly recommend you download
that explains the process pretty well. You can also call the help desk for
guidance.
The baseline energy usage can and often does increase when the ASHRAE 62.1
calculation is properly applied because the presence of critical zones with high
occupant density, like conference rooms, will set the OA percentage for an
entire AHU. All the rooms fed by that AHU will have that same OA percentage and
thus some rooms will receive more OA than a simple calculation (as is done by
"Sum Room OAReqs" on the advanced systems tab). This increase in OA will
increase the energy consumption. If you selectively over air the critical zones
to lower the OA percentage at the AHU, which is the accepted procedure, then the
supply air will increase leading to increased fan and reheat energy.
This ASHRAE 62.1 feature and the DCV calculation is one of the best advantages
that Trace has over other programs like Equest that cannot do the ASHRAE 62.1
calculation properly. The Trace program can both design and model HVAC system
OA requirements properly. It also can be used to properly design and model DOAS
units including capturing the sensible and latent cooling provided. I have not
seen any program that can model DCV or OA better than Trace if you use it
properly.
I have used Trace to document DCV savings in LEED project submissions without
difficulty. It just needs to be used properly.
Rick
R I C H A R D E L L I S O N
PE, BEMP, CEM, CEA, CTAB, CBEP, LEED AP
Manager Energy and Modeling
Southland Industries
22340 Dresden Street, Suite 177
Dulles, VA 20166
Office: 703.834.5570
Direct: 703.834.2438
Fax: 703.834.5572
From:trace-users-bounces at lists.onebuilding.org
[mailto:trace-users-bounces at lists.onebuilding.org] On Behalf Of Julia Beabout
Sent: Monday, August 30, 2010 9:20 AM
To: Jen Redington; trace-users at lists.onebuilding.org
Subject: Re: [Trace-users] Demand Controlled Ventilation
Hi Jen,
I agree. That does sound fishy. Generally, I do not use the DCV control
feature within Trace to calc my energy savings from DCV. Some LEED reviewers
have questioned using it as well. It's not that the algorithm is not correct
its just that applying it to a real project can be tricky and require some level
of judgment that the software doesn't know about. Similarly, I rarely use the
ASHRAE 62 calc capabilities in Trace to simulate that calc. Except of the
simplest of situations the calc can be thrown off very easily. One room can
throw off the whole calc, so some judgment and adjustment is needed ....in my
experience, it frequently take more time to comb through the calcs to figure out
which spaces are throwing off the calc than to estimate the savings via other
means. I still estimate both with in Trace so it doesn't count as an
exceptional calculation for LEED but I don't use Trace's built in routines to do
it.
For DCV, based on the occupancy schedules for the spaces with DCV, I calc and
make an adjusted OA schedule for those spaces. This is actually a lot less work
and easier than it sounds.
Similarly, for the ASHRAE 62 calc, I do it on a spreadsheet and then force that
cfm value at the system level in Trace (System level, Options Tab, Advanced
options button). If you have a VAV system that needs an ASHRAE 62 calc and you
are using DCV in some spaces, then you will need to adjust the system level OA
schedule to reflect the DCV.
You can check to see that the program is bringing the correct OAcfm and adjust
the schedule as needed by reviewing the cfms via the View Reports, Analysis tab,
Graph Profiles and Energy button. Once there, In the view menu, turn on the
"settings" menu and switch to the "table" view. Then you can navigate the
settings on the left side of the screen to get Trace to display the cfms of the
AHU/system(s) in question. (You could also use this viewing feature to review
what Trace did with the OAcfm when you used the automatic DCV and/or ASHRAE 62
calc within Trace to help find clues as to what's going on and if indeed Trace
is simulating those features and the OAcfm correctly).
Again, the manual adjusted schedules and forced cfm method may sound difficult
and like a lot of work, but it's not really. Once you do it once, you're done.
And, it gives you a confidence level that Trace is simulating the OAcfm
correctly.
Hope that helps.
Julia
________________________________
From:Jen Redington <redington at vitetta.com>
To: trace-users at lists.onebuilding.org
Sent: Mon, August 30, 2010 8:15:32 AM
Subject: [Trace-users] Demand Controlled Ventilation
I am doing an energy model for LEED and added demand controlled ventilation to
several spaces in both the design and baseline models. This doubled my energy
cost savings for the project. The space heating gas use went down 25% in the
design model but doubled in the baseline model. I can’t see any reason why the
baseline energy use would increase, and the savings in the design case seem a
little unrealistic since DCV is only being used in some spaces. Any ideas what
could be wrong? Any one else have any similar issues?
Thanks,
Jen Redington
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/trace-users-onebuilding.org/attachments/20100831/e89b5963/attachment-0002.htm>
More information about the Trace-users
mailing list