[Equest-users] Chilled Water Heat Pump Modeling

Brian Fountain Brian.Fountain at sa-footprint.com
Mon Dec 22 11:08:17 PST 2025


Note that Bill's solution is for 2.3 where the loop type "well" has been removed as a requirement for the loop-to-loop heat pump ... and has been removed from the DOE-2.3 entirely.

From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Bill Bishop via Equest-users
Sent: December 22, 2025 1:35 PM
To: Jeff Ross-Bain <jeff at rbgb.com>; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Chilled Water Heat Pump Modeling

CAUTION: This message originated from outside Smith + Andersen
________________________________
Hi Jeff,

For the CW-LOOP of your LOOP-TO-LOOP-HP chiller(s), use a WLHP loop. Assuming your HP chiller is water-cooled, you then connect boilers and heat-rejection to the loop. If the HP chiller is air-cooled, you can't use the LOOP-TO-LOOP-HP type.
You may choose to model the preheat and reheat coils as separate HW loops. If you model them as additional primary HW loops, you would serve them with the boilers per the design. Or you can model secondary HW loops off of the LOOP-TO-LOOP-HP HW loop.

Regards,
~Bill

William Bishop, PE, CEM, LEED AP, ASHRAE (BEMP, BEAP, CDP)
Associate Principal | Project Executive | Sustainability & Energy
[now IMEG]<https://url.ca.m.mimecastprotect.com/s/vJd3C81ZVmIOOA4Kunf8FyJQyJ/>
IMEG | formerly Pathfinder                                                 (585) 698-1956 | phone
134 South Fitzhugh Street | Rochester, NY 14608               (315) 879-1122 | mobile
William.J.Bishop at imegcorp.com<mailto:William.J.Bishop at imegcorp.com>  website<https://url.ca.m.mimecastprotect.com/s/qCqNC91ZWnIRR67pSEhjFqOgw-/> | vCard<https://dynasend.com/signatures/vcard/William.J.Bishop-at-imegcorp.com.vcf> | map<https://www.google.com/maps/place/Pathfinder+Engineers+%26+Architects+LLP/@43.1504815,-77.6145058,17z/data=!3m1!4b1!4m6!3m5!1s0x89d6b4fe9e48aab1:0x6991ae3d559d5aee!8m2!3d43.1504776!4d-77.6119309!16s%2Fg%2F1tcw955j?hl=en&entry=ttu>          [Twitter] <https://url.ca.m.mimecastprotect.com/s/dsRjCjZr1ySllwNvt1tqFmF7Ub/>  [Facebook] <https://url.ca.m.mimecastprotect.com/s/3cFNCk8v1ziYYRGpc8uoFGCGRz/>   [LinkedIn] <https://www.linkedin.com/company/imeg-corp>
Learn more<https://url.ca.m.mimecastprotect.com/s/uWbrCmOx5BC1174rh3FgFR-5Ug/> about us and the IMEG story!   Ride your bike!  [A person on a motorcycle  Description automatically generated]

From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Jeff Ross-Bain via Equest-users
Sent: Monday, December 22, 2025 9:19 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Chilled Water Heat Pump Modeling

External Email: Treat links and attachments with caution.
Dear eQUEST Brain Trust:

I am trying to model a chilled water heat pump using the "loop to loop" approach and have reached a point where I know not where to go...

The rules call for the heat pump condenser to be linked to a Lake/Well loop. The system also has boilers attached to the system preheat coil and to the zone reheat coils, in a sort of supplemental format for when the HP chiller cannot meet set points.
I can create all the loops, with associated pumps, yet the lake/well loop requires a heat source. I cannot determine how to do that (after hours and hours!), or if I am missing something.

Does anyone know of a procedure for modeling this situation (besides the eQUEST help pages)? I wonder if the boilers may be part of the issue.

Many thanks to everyone and wish you all the happiest of holidays.

Regards,

Jeff Ross-Bain, PE, LEED Fellow, WELL AP, BCxP, BEMP, HBDP
President

[cid:image015.jpg at 01DC734C.6669C9F0]<https://url.ca.m.mimecastprotect.com/s/CaPDCnxy1DCll1BYtvHxFJVrDL/>

Atlanta:  404-220-8955
Charleston:  843-779-9229
www.rbgb.com<https://url.ca.m.mimecastprotect.com/s/CaPDCnxy1DCll1BYtvHxFJVrDL/>
Maximizing Building Performance

[A logo with a leaf and text  AI-generated content may be incorrect.]

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20251222/7c6a94e3/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.jpg
Type: image/jpeg
Size: 2024 bytes
Desc: image008.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20251222/7c6a94e3/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 420 bytes
Desc: image009.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20251222/7c6a94e3/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.png
Type: image/png
Size: 342 bytes
Desc: image010.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20251222/7c6a94e3/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image011.png
Type: image/png
Size: 387 bytes
Desc: image011.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20251222/7c6a94e3/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image013.jpg
Type: image/jpeg
Size: 890 bytes
Desc: image013.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20251222/7c6a94e3/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image015.jpg
Type: image/jpeg
Size: 3125 bytes
Desc: image015.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20251222/7c6a94e3/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image016.jpg
Type: image/jpeg
Size: 2876 bytes
Desc: image016.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20251222/7c6a94e3/attachment-0003.jpg>


More information about the Equest-users mailing list