Hello,
I’m currently modeling a VRF system in eQUEST 7175. The equipment cut
sheets include both cooling EER and heating COP values. However, I
noticed that the VRF condensing unit input in eQUEST only allows for
cooling efficiency—there’s no direct field for heating COP.
I looked into this and wasn’t able to find any documentation or
settings that allow for a direct input of heating COP.
Here’s the approach I’ve taken to work around this:
For compressor energy consumption in cooling, heating, or combined
modes, I’m using the following formula:
P = Prated × EIR_FPLR × EIR_FT × CAP_FT
The default performance curves applied are:
VRF044-Cap-fSST&SDT
VRF044-EIR-fSST&SDT
VRF044-EIR-fPLR
Energy consumption is calculated as follows:
At cooling SST & SDT → based on cooling EER
At heating SST & SDT → based on heating COP
So, instead of directly inputting both cooling and heating EIR values,
I rely on:
Cooling EIR
Cooling SST & SDT (used to calibrate the default curve)
Heating SST & SDT (used to reflect heating performance through the
same default curve)
A detailed breakdown of the calculations is provided in the attached Excel file.
-------------- next part --------------
A non-text attachment was scrubbed...
Name: VRF COP INPUT.xlsx
Type: application/vnd.openxmlformats-officedocument.spreadsheetml.sheet
Size: 90105 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20250822/9c56faf2/attachment.xlsx>
More information about the Equest-users
mailing list