[Equest-users] Changing Ventilation Rate for some months in the year
    Seaman, Ethan 
    eseaman at smma.com
       
    Fri Sep 29 04:35:57 PDT 2023
    
    
  
Ahmad,
Are you trying to vary the system CFM or OA CFM?  See below for eQuest’s definition of Minimum OA Sch.  The minimum OA schedule varies the hourly OA ratio.  To create an annual schedule to vary the CFM seasonally you can create an additional set of weekly/daily schedules, and then set the run times in the annual schedule.
[cid:image001.png at 01D9F2A7.51D23090]
_______________________________________________
Ethan Seaman
Sustainable Design Analyst
SMMA
t: 617.520.9288
www.smma.com
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Ahmad Fraij via Equest-users
Sent: Friday, September 29, 2023 6:16 AM
To: equest-users at onebuilding.org
Subject: Re: [Equest-users] Changing Ventilation Rate for some months in the year
Hello Guys,
Did  anyone have a chance to review my question in my email below?
I found the option to add "Minimum OA Schedule" but this schedule is fraction of what? Is it fraction of the CFM/person values that we enter in the Zones? I have added this schedule and changed the fractions and the energy consumption and the heating loads have been changed but the OA air flow rate & ratio in the report SV-A has not changed? Am I missing something?
If the "Minimum OA Schedule" changes the OA flow rate, then where can I find this value? I am trying to change the OA flow rate for a specific value for only three months per year for pandemic mitigation so how can I do that?
Any help will be highly appreciated
Regards
Ahmad
On Thursday, 28 September 2023 at 04:29:56 pm AEST, Ahmad Fraij <fraij at yahoo.com> wrote:
Hello Guys,
How can I change the ventilation rate for a building in eQUEST software for only three months of the year (Dec, Jam & Feb)?
Your help will be highly appreciated.
Regards
Ahmad
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20230929/0eff72eb/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 35007 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20230929/0eff72eb/attachment.png>
    
    
More information about the Equest-users
mailing list