    Fri Sep 15 11:10:53 PDT 2023
    
    
  
Ahmad,
I believe you’re looking for the following:
LS-C Building Peak Load Components
LS-D Building Monthly Loads Summary
_______________________________________________
Ethan Seaman
Sustainable Design Analyst
SMMA
t: 617.520.9288
www.smma.com
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Ahmad Fraij via Equest-users
Sent: Thursday, September 14, 2023 4:11 AM
To: equest-users at onebuilding.org
Subject: [Equest-users] Simulation Report for Building Peak Loads
Hello,
Which simulation report in eQUEST gives the monthly building peak cooling and heating loads. I am talking about the building space loads and not the HVAC system loads. We are improving the envelop of one of the buildings and we need to see the impact on the monthly peak cooling and heating loads.
Thanking you very much for the help.
Regards