[Equest-users] Zones with Insufficient Heating Capability
    Haberl, Jeff 
    jhaberl at tamu.edu
       
    Wed Sep  6 06:43:49 PDT 2023
    
    
  
Hello Chad:
Sounds like you've got yourself in a pickle. Although you only have 24 zones, you don't know which one is causing the trouble. However, the key thing to remember is that this is a simulation that follows specific rules. So, it may or may not represent the building you're simulating.
I'd start by resetting all systems back to SYSTEM = SUM and see if this works. What you'll have at this point is the loads on the systems, but not the system reactions themselves. If this doesn't work then you have an issue with your zone assignments or space loads. If it does work, then you can add back into the simulation each system, one at a time, until you find the offending system. Remember to let DOE-2 autosize.
Or, you could just us a VAV for all 24 zones and see if this works...then go back to separating it out the systems.
Jeff
Jeff S. Haberl, Ph.D., P.E.inactive, FASHRAE, FIBPSA               We are like fluttering leaves on the branches of trees
Liz & Nelson Mitchell Professor in Residential Design           in the forest of the landscape that surrounds us.
Department of Architecture                                                       If we could, for just a moment, flutter together,
Texas A&M University                                                                  we could lift the earth up to be a better place.  JSH 2022
College Station, TX 77845-3581
Office: 979-845-6507, Lab: 979-845-6065
Fax 979-862-2457
jhaberl at tamu.edu,www.esl.tamu.edu<mailto:jhaberl at tamu.edu,www.esl.tamu.edu>
________________________________
From: Equest-users <equest-users-bounces at lists.onebuilding.org> on behalf of Chad Langille via Equest-users <equest-users at lists.onebuilding.org>
Sent: Tuesday, September 5, 2023 7:53 PM
To: equest-users at lists.onebuilding.org <equest-users at lists.onebuilding.org>
Subject: [Equest-users] Zones with Insufficient Heating Capability
Hi All, I’m working on a multi-level recreation building with VRF serving offices on each floor and packaged RTUs with DX cooling/furnace heating serving large open convention spaces per floor. I ran into this issue without changing anything
ZjQcmQRYFpfptBannerStart
This Message Is From an External Sender
This message came from outside your organization.
ZjQcmQRYFpfptBannerEnd
Hi All,
I’m working on a multi-level recreation building with VRF serving offices on each floor and packaged RTUs with DX cooling/furnace heating serving large open convention spaces per floor.
I ran into this issue without changing anything in my model, besides adding some exhaust fan information to a handful of zones:
This box pops up:
[cid:image001.png at 01D9E01F.9E4BDC40]
“Error: 1 standard file writing errors encountered”
The simulation does not run, and in the Detailed Simulation Output File, 24 zones have the following warning:
**WARNING**********************************************************************
             ZONE E2 Core Zn (G.C10)
             might have insufficient heating capability.
             Check that the SYSTEM or ZONE HEATING-CAPACITY plus this
             ZONEs BASEBOARD-RATING is adequate to maintain the ZONE
             specified DESIGN-HEAT-T for the calculated peak ZONE load
             (see LS-A or LS-B for the ZONE peak load.)
I increased my throttling rage from 2 to 6 degrees, tried increasing my Heating Control and Reset Zone Entering Max Supply Temp from 90 to 105 degrees under Zone Heating, Coil Cap / Control, tried forcing previously greyed-out n/a to 50 degrees for reheat delta T, and tried changing thermostat to Reverse Action. No change and I’m out of ideas. Any assistance would be greatly appreciated!
Thank you,
Chad
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20230906/c2b5b123/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 4715 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20230906/c2b5b123/attachment.png>
    
    
More information about the Equest-users
mailing list