[Equest-users] Cooling & Heating Hours in eQUEST Software
Brian Fountain
bfountain at greensim.com
Mon Jul 24 05:40:26 PDT 2023
SS-C gives you heating and cooling hours system by system
SS-E gives you building level heating and cooling hours. SS-D gives peak and total loads.
If your systems are hydronic, PS-D gives you the loop loads and hours. PS-C gives you annual boiler and chiller runtimes. PS-H gives the same loop and equipment information but monthly.
On Jul 24, 2023, 7:33 AM, at 7:33 AM, Ahmad Fraij via Equest-users <equest-users at lists.onebuilding.org> wrote:
>Hello,
>Does any body know where can I get the annual cooling hours and heating
>hours in eQUEST software? i.e. how many hours per year does the cooling
>system operate and how many hours per year does the heating system
>operate?
>I have a building with multi-levels and each level has multi-zones.
>Is there a simulation report that gives these hours?
>Regards
>Ahmad
>
>------------------------------------------------------------------------
>