[Equest-users] DHW Load Exceeding DHW Capacity
Nicholas CATON
Nicholas.Caton at se.com
Mon Apr 10 02:34:54 PDT 2023
Hi Chris,
I’m a little rusty on how this might be different for DHW loops vs. HHW loops/boilers (it’s been some years since I did building energy simulations on the regular), but I’ve definitely modeled DHW systems on HHW loops if that’s pertinent.
What I recall is:
1. If needed, you can define and/or adjust the DHW loop’s (process) load schedule as-generated by the Wizards (which in kind will develop a single schedule for a project considering a weighted average of building occupancy types from your shell input screens).
2. As for sequencing, my intuition is that before you do anything additional (like define an EQUIP-CTRL command and/or set up a LOAD-MANAGEMENT), eQuest/doe2 will by default and generally
* Activate the minimum number of loop-connected machines to satisfy the load of the moment, and will evenly distribute that load between those machines.
* Assuming your primary equipment has different capacities, it’ll work out each interval what combination of equipment capacities “best fit” the load on the loop and consider those machines active
* Assuming your primary equipment has equal capacities, it’ll engage the equipment in the order it’s defined, without trying to equalize runtime or similar.
* All of this may not be the most efficient sequence or otherwise reflect real-world design or installed conditions, but it’s typically a safe starting point assuming attached machines are of a similar type/vintage.
3. If you need/want to more explicitly define or revise default equipment staging behavior, then IIRC it’s good advice to try and accomplish that with an EQUIP-CTRL alone first, as combining with a LOAD-MANAGEMENT command can open up new options but can also grow unnecessarily complicated in practice, at least sometimes.
If you are observing loads in excess of an individual actual boiler’s capacity, without engaging a second unit, I would start with reviewing the boiler’s capacity input. Wizard-generated projects often allow primary hydronic equipment to auto-size to the load of the loop, in which case you’ll observe a blank field you need to input to specify rated capacity of the equipment. From there, assuming you have something input to cap or at least assert design capacity, both DW and HW boilers have inputs which allow for further restricting ratios of output beyond design and/or asserting minimum operating ratios, which could be fruitful to explore depending on context specific to your model and how it’s set up.
If your hard capacity limits for the equipment are not able to keep up with the loop load in a sustained/substantial fashion, I think you can expect to see something corroborating that effect in the detailed simulation report ATTN messages as a CAUTION and/or WARNING. IIRC there are also “overload” hours that should be noted in one or more of the PS reports.
If everything seems to check out after reviewing capacity related inputs and additional units are just not engaging, I might next suspect and look into either loop inputs and/or user-generated sequence inputs resulting in making one or more primary equipment units unavailable in the simulation.
~Nick
[cid:image001.jpg at 01D96BD1.E4E24030]
Nick Caton, P.E. (US), BEMP
ニック ケートン, P.E. (US), BEMP
Senior Energy Engineer
Energy Manager, Yokota Airbase
ESS - Energy & Sustainability Services
M JP
M US
DSN
Email
+81 . 070 . 3366 . 3317
+1 . 785 . 410 . 3317
315 . 225 . 1672
nicholas.caton at se.com<mailto:nicholas.caton at se.com>
シニアエネルギーエンジニア
横田基地エネルギーマネージャー
ESS - エナジー持続可能性サービス
[cid:image002.png at 01D96BD1.E4E24030]
[cid:image003.png at 01D96BD1.E4E24030]
[cid:image001.jpg at 01D96BD1.E4E24030]
Internal
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Chris Hadlock via Equest-users
Sent: Thursday, April 6, 2023 6:23 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] DHW Load Exceeding DHW Capacity
[External email: Use caution with links and attachments]
________________________________
Does anyone know why eQuest allows my DHW assigned load to exceed my DHW capacity in eQuest 3.65 (7175) DOE 2.3.
My project has 4 DHW boilers sequenced using parallel configuration. I'm looking at an hourly report and there are hours of the day where the load is 470 MBH and my first boiler is assigned a load of 470 MBH while its operating capacity is 392 MBH. No other boilers are active for that hour. Does some of that unmet load get carried over to the next hour?
Also, does anyone know how eQuest decides which DHW boiler (for multiple boilers in parallel configuration) is active for any given hour?
Thanks,
Chris
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20230410/437caa32/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1794 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20230410/437caa32/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 1819 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20230410/437caa32/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 6024 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20230410/437caa32/attachment-0001.png>
More information about the Equest-users
mailing list