[Equest-users] Dual Duct with package Cooling

David Eldridge DEldridge at grummanbutkus.com
Wed Jun 15 08:16:06 PDT 2022


For those reading but still wondering what we're talking about, here are some system descriptions and schematics from this application guide from York.
Multizone Application of Solution Units (johnsoncontrols.com)<https://www.johnsoncontrols.com/-/media/jci/be/united-states/airside-systems/air-handling-units/files/be_appguide_multizone_ahu.pdf?la=en&hash=6E1545B6DDE404270B6FA63B3B32AAB607C17414>

As infrequently as we see multizone units still running, an even smaller group of them need to be modeled in a whole building modeling program so it's getting kind of rare to model one. Most of these are smaller and would be replaced without a modeling effort.

There are a few of the larger DD systems still out there as deep retrofit candidates so maybe more likely to be modeled. I've got my eye on one in particular.

David


David S. Eldridge, Jr., P.E., BEMP, BEAP, HBDP, GGF/A
Direct: (847) 316-9224 | Mobile: (773) 490-5038

Grumman|Butkus Associates | 820 Davis Street, Suite 300 | Evanston, IL 60201
Energy Efficiency Consultants and Sustainable Design Engineers

grummanbutkus.com<http://grummanbutkus.com/> | Facebook<https://www.facebook.com/pages/GrummanButkus-Associates/1385285015032526> | Twitter<https://twitter.com/grummanbutkus> | LinkedIn<https://www.linkedin.com/company/102242?trk=tyah&trkInfo=clickedVertical%3Acompany%2CclickedEntityId%3A102242%2Cidx%3A2-3-6%2CtarId%3A1445536322603%2Ctas%3Agrumman>



________________________________
From: Melissa Crowe <MCrowe at cmta.com>
Sent: Wednesday, June 15, 2022 8:45:50 AM
To: David Eldridge <DEldridge at grummanbutkus.com>; John Aulbach <jra_sac at yahoo.com>; equest-users at lists.onebuilding.org <equest-users at lists.onebuilding.org>
Subject: RE: [Equest-users] Dual Duct with package Cooling


I have learned something. Thank you.  I have actually never had to model a system like that but you are correct, I have looked at them all but misunderstood the Multizone.  I see there are actually several dual duct systems.   Packaged Multi zone is DX, Multizone is CHW and then there is Dual Duct CHW.



Say something ignorant...learn something new.









Melissa Crowe, BEMP, LEED AP

Sr Mechanical/Energy Engineer

[cid:image001.png at 01D8809B.BE2FF5D0]<https://nam11.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.cmta.com%2F&data=05%7C01%7CMCrowe%40cmta.com%7Cee9dc156e1f248123f2808da29e84448%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637868374796753279%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=gn955gOnIqvl6WsiUQEJ1mSVzguQnJKsZbrH4ZyxJI8%3D&reserved=0>

161 Worcester Road, Suite 305

Framingham, MA 01701

O: 508.647.9200

C: 978-204-2559

cmta.com<https://nam11.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.cmta.com%2F&data=05%7C01%7CMCrowe%40cmta.com%7Cee9dc156e1f248123f2808da29e84448%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637868374796753279%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=abW0hcCD%2BQpbv%2Bxf9bgvUZzg9r8CorSMs8fQybOtQL8%3D&reserved=0>

[cid:image002.png at 01D8809B.BE2FF5D0]<https://nam11.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2FCMTAEngineers%2F&data=05%7C01%7CMCrowe%40cmta.com%7Cee9dc156e1f248123f2808da29e84448%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637868374796753279%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=1VLG8OOlZ8is5kueNEJhZPnCujkVL14MW6OPhzGCLeA%3D&reserved=0>[cid:image003.png at 01D8809B.BE2FF5D0]<https://nam11.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fcompany%2Fcmta-inc.&data=05%7C01%7CMCrowe%40cmta.com%7Cee9dc156e1f248123f2808da29e84448%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637868374796753279%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=r5UGD6%2BIgCa1b6g1yAXNEAmPdLSLAphb1eM1hFBtc6k%3D&reserved=0>[cid:image004.png at 01D8809B.BE2FF5D0]<https://nam11.safelinks.protection.outlook.com/?url=https%3A%2F%2Ftwitter.com%2FCMTAEngineers&data=05%7C01%7CMCrowe%40cmta.com%7Cee9dc156e1f248123f2808da29e84448%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637868374796753279%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=BcV%2BFkHlCUc%2B19OYtvyyrcJY9KpbTVoM7p%2F%2F2psASn0%3D&reserved=0>





From: David Eldridge <DEldridge at grummanbutkus.com>
Sent: Tuesday, June 14, 2022 7:25 PM
To: Melissa Crowe <MCrowe at cmta.com>; John Aulbach <jra_sac at yahoo.com>; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Dual Duct with package Cooling





EXTERNAL SENDER: This email originated outside of CMTA. Do not click links or open attachments unless you know the sender and know the content is safe.



It is - this is a multizone system with hot deck and cold deck where it blends the two airflows to satisfy the zones, taking constant flow overall with proportion of cold and hot deck air. The mixing takes place at the AHU though and a single duct goes out to the zone as opposed to the dual-duct approach. The size of the units is limited since there isn't enough room for ductwork branches, I've usually seen these from three to seven zones. So in that regard it makes sense for a DX although I've mostly seen these in university buildings which do have CHW and HW or steam, sometimes at hotels.



For the dual-duct AHU where the mixing takes place at the zone, you can have a much higher number of zones since the space isn't constrained at the discharge air location so I can see that DD AHUs I've seen would be very large and tend to be CHW and HW/Steam and not DX.



So I think it's probably the best approximation to use the multizone template.



The chiller idea would give another approach but could have part load performance different than the DX system would have, but also a way to attempt a workaround.



David





David S. Eldridge, Jr., P.E., BEMP, BEAP, HBDP, GGF/A

Direct: (847) 316-9224 | Mobile: (773) 490-5038



Grumman|Butkus Associates | 820 Davis Street, Suite 300 | Evanston, IL 60201

Energy Efficiency Consultants and Sustainable Design Engineers



grummanbutkus.com<https://nam11.safelinks.protection.outlook.com/?url=http%3A%2F%2Fgrummanbutkus.com%2F&data=05%7C01%7CMCrowe%40cmta.com%7C0a1dc0c1420e4f3973c108da4e5d2151%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637908459166212813%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=Ma9pfP%2BS8u9tWQEKXZSDpUkq4iOFspIT7fzV%2BnKRXvw%3D&reserved=0> | Facebook<https://nam11.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FGrummanButkus-Associates%2F1385285015032526&data=05%7C01%7CMCrowe%40cmta.com%7C0a1dc0c1420e4f3973c108da4e5d2151%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637908459166212813%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=m6AtotiKeHArS1alSX8HGv5P4NxTZljwI%2BGg6juZhRE%3D&reserved=0> | Twitter<https://nam11.safelinks.protection.outlook.com/?url=https%3A%2F%2Ftwitter.com%2Fgrummanbutkus&data=05%7C01%7CMCrowe%40cmta.com%7C0a1dc0c1420e4f3973c108da4e5d2151%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637908459166212813%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=xn73wzWdptvB%2FqtXklurosUWzWkYrU1segAslyxk2Jw%3D&reserved=0> | LinkedIn<https://nam11.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fcompany%2F102242%3Ftrk%3Dtyah%26trkInfo%3DclickedVertical%253Acompany%252CclickedEntityId%253A102242%252Cidx%253A2-3-6%252CtarId%253A1445536322603%252Ctas%253Agrumman&data=05%7C01%7CMCrowe%40cmta.com%7C0a1dc0c1420e4f3973c108da4e5d2151%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637908459166212813%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=Em8PegOPCGK%2FItXwPJ3wSLA%2BVQM5Cx5QPtRVqO5cZHg%3D&reserved=0>



From: Melissa Crowe <MCrowe at cmta.com<mailto:MCrowe at cmta.com>>
Sent: Tuesday, June 14, 2022 4:15 PM
To: David Eldridge <DEldridge at grummanbutkus.com<mailto:DEldridge at grummanbutkus.com>>; John Aulbach <jra_sac at yahoo.com<mailto:jra_sac at yahoo.com>>; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: [Equest-users] Dual Duct with package Cooling



I replied too fast the multi zone is only DX will not allow CHW.



However this is not thermally equivalent to Dual Duct where you can cool one zone while heating the other with out reheating.





Melissa Crowe, BEMP, LEED AP

Sr Mechanical/Energy Engineer

[cid:image001.png at 01D8809B.BE2FF5D0]<https://nam11.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.cmta.com%2F&data=05%7C01%7CMCrowe%40cmta.com%7C0a1dc0c1420e4f3973c108da4e5d2151%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637908459166212813%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=WA%2FXtwA1C6JIpj9jz9CSQ9o%2BBlIaHI8L%2FW90zkPjFtY%3D&reserved=0>

161 Worcester Road, Suite 305

Framingham, MA 01701

O: 508.647.9200

C: 978-204-2559

cmta.com<https://nam11.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.cmta.com%2F&data=05%7C01%7CMCrowe%40cmta.com%7C0a1dc0c1420e4f3973c108da4e5d2151%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637908459166212813%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=AO6qyTPATmScJvdCFQZ2DqnayrywxYNWMhfVbTb8kxM%3D&reserved=0>

[cid:image002.png at 01D8809B.BE2FF5D0]<https://nam11.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2FCMTAEngineers%2F&data=05%7C01%7CMCrowe%40cmta.com%7C0a1dc0c1420e4f3973c108da4e5d2151%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637908459166212813%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=OeKe551a92hPwkMZjTrN9ZbJfsZH%2Bq3JKG5gq7UbHwY%3D&reserved=0>[cid:image003.png at 01D8809B.BE2FF5D0]<https://nam11.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fcompany%2Fcmta-inc.&data=05%7C01%7CMCrowe%40cmta.com%7C0a1dc0c1420e4f3973c108da4e5d2151%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637908459166212813%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=shgvlvV0zXjy6J1fh0%2FSPzNhbwJtHIXIhEh6EzWUvao%3D&reserved=0>[cid:image004.png at 01D8809B.BE2FF5D0]<https://nam11.safelinks.protection.outlook.com/?url=https%3A%2F%2Ftwitter.com%2FCMTAEngineers&data=05%7C01%7CMCrowe%40cmta.com%7C0a1dc0c1420e4f3973c108da4e5d2151%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637908459166212813%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=YerW0DXWb%2F1vFoiGk9vMRtCYNkCESj72D2WDjCUZq5E%3D&reserved=0>





From: David Eldridge <DEldridge at grummanbutkus.com<mailto:DEldridge at grummanbutkus.com>>
Sent: Tuesday, June 14, 2022 5:06 PM
To: Melissa Crowe <MCrowe at cmta.com<mailto:MCrowe at cmta.com>>; John Aulbach <jra_sac at yahoo.com<mailto:jra_sac at yahoo.com>>; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: [Equest-users] Dual Duct with package Cooling



You don't often get email from deldridge at grummanbutkus.com<mailto:deldridge at grummanbutkus.com>. Learn why this is important<https://aka.ms/LearnAboutSenderIdentification>



EXTERNAL SENDER: This email originated outside of CMTA. Do not click links or open attachments unless you know the sender and know the content is safe.



Does it let you pick DX for the multizone AHU type?



David





David S. Eldridge, Jr., P.E., BEMP, BEAP, HBDP, GGF/A

Direct: (847) 316-9224 | Mobile: (773) 490-5038



Grumman|Butkus Associates | 820 Davis Street, Suite 300 | Evanston, IL 60201

Energy Efficiency Consultants and Sustainable Design Engineers



grummanbutkus.com<https://nam11.safelinks.protection.outlook.com/?url=http%3A%2F%2Fgrummanbutkus.com%2F&data=05%7C01%7CMCrowe%40cmta.com%7C0a1dc0c1420e4f3973c108da4e5d2151%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637908459166212813%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=Ma9pfP%2BS8u9tWQEKXZSDpUkq4iOFspIT7fzV%2BnKRXvw%3D&reserved=0> | Facebook<https://nam11.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FGrummanButkus-Associates%2F1385285015032526&data=05%7C01%7CMCrowe%40cmta.com%7C0a1dc0c1420e4f3973c108da4e5d2151%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637908459166212813%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=m6AtotiKeHArS1alSX8HGv5P4NxTZljwI%2BGg6juZhRE%3D&reserved=0> | Twitter<https://nam11.safelinks.protection.outlook.com/?url=https%3A%2F%2Ftwitter.com%2Fgrummanbutkus&data=05%7C01%7CMCrowe%40cmta.com%7C0a1dc0c1420e4f3973c108da4e5d2151%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637908459166212813%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=xn73wzWdptvB%2FqtXklurosUWzWkYrU1segAslyxk2Jw%3D&reserved=0> | LinkedIn<https://nam11.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fcompany%2F102242%3Ftrk%3Dtyah%26trkInfo%3DclickedVertical%253Acompany%252CclickedEntityId%253A102242%252Cidx%253A2-3-6%252CtarId%253A1445536322603%252Ctas%253Agrumman&data=05%7C01%7CMCrowe%40cmta.com%7C0a1dc0c1420e4f3973c108da4e5d2151%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637908459166212813%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=Em8PegOPCGK%2FItXwPJ3wSLA%2BVQM5Cx5QPtRVqO5cZHg%3D&reserved=0>



From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Melissa Crowe via Equest-users
Sent: Tuesday, June 14, 2022 3:19 PM
To: John Aulbach <jra_sac at yahoo.com<mailto:jra_sac at yahoo.com>>; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Dual Duct with package Cooling



Hi John



If by packaged Cooing you mean Air Cooled DX then, how about trying:

  *   Dual Duct system w. CHW
  *   "Chiller" =  Air cooled with appropriate compressor type (recip or scroll) and count
  *   Pump power = 0
  *   CHW supply temperature = ~ DX evaporator T



Good luck



Melissa Crowe, BEMP, LEED AP

Sr Mechanical/Energy Engineer

[cid:image001.png at 01D8809B.BE2FF5D0]<https://nam11.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.cmta.com%2F&data=05%7C01%7CMCrowe%40cmta.com%7C0a1dc0c1420e4f3973c108da4e5d2151%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637908459166212813%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=WA%2FXtwA1C6JIpj9jz9CSQ9o%2BBlIaHI8L%2FW90zkPjFtY%3D&reserved=0>

161 Worcester Road, Suite 305

Framingham, MA 01701

O: 508.647.9200

C: 978-204-2559

cmta.com<https://nam11.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.cmta.com%2F&data=05%7C01%7CMCrowe%40cmta.com%7C0a1dc0c1420e4f3973c108da4e5d2151%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637908459166212813%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=AO6qyTPATmScJvdCFQZ2DqnayrywxYNWMhfVbTb8kxM%3D&reserved=0>

[cid:image002.png at 01D8809B.BE2FF5D0]<https://nam11.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2FCMTAEngineers%2F&data=05%7C01%7CMCrowe%40cmta.com%7C0a1dc0c1420e4f3973c108da4e5d2151%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637908459166212813%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=OeKe551a92hPwkMZjTrN9ZbJfsZH%2Bq3JKG5gq7UbHwY%3D&reserved=0>[cid:image003.png at 01D8809B.BE2FF5D0]<https://nam11.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fcompany%2Fcmta-inc.&data=05%7C01%7CMCrowe%40cmta.com%7C0a1dc0c1420e4f3973c108da4e5d2151%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637908459166212813%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=shgvlvV0zXjy6J1fh0%2FSPzNhbwJtHIXIhEh6EzWUvao%3D&reserved=0>[cid:image004.png at 01D8809B.BE2FF5D0]<https://nam11.safelinks.protection.outlook.com/?url=https%3A%2F%2Ftwitter.com%2FCMTAEngineers&data=05%7C01%7CMCrowe%40cmta.com%7C0a1dc0c1420e4f3973c108da4e5d2151%7C7bb63ee7a3e14d75b5a56f9549f171a3%7C0%7C0%7C637908459166212813%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C3000%7C%7C%7C&sdata=YerW0DXWb%2F1vFoiGk9vMRtCYNkCESj72D2WDjCUZq5E%3D&reserved=0>





From: John Aulbach <jra_sac at yahoo.com<mailto:jra_sac at yahoo.com>>
Sent: Tuesday, June 14, 2022 1:54 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Dual Duct with package Cooling



A friend of mine asked me about such a system. I looked it up, and lo and behold, eQuest doesn't this as a system.



Is there any equivalent system that can dynamically mimic this?



Thanks,



John R. Aulbach, PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20220615/32480a9a/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 6481 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20220615/32480a9a/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 1796 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20220615/32480a9a/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 2025 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20220615/32480a9a/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 1901 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20220615/32480a9a/attachment-0003.png>


More information about the Equest-users mailing list