[Equest-users] Gas Consumption Difference

Ahmad Fraij fraij at yahoo.com
Thu Nov 11 02:58:53 PST 2021


 Thanks Brian for the help and the clarification. Is there a way to reduce the scale of the results from 1,000,000,000 to 1,000,000 in the results report?
Regards
Ahmad 

On Thursday, 11 November 2021, 09:30:35 pm AEDT, Brian Fountain <brian.fountain at sa-footprint.com> wrote: 
 
 
Your results are shown as 5.54 x 109 BTU or 5,540 MBTU in the .pdf.  The capture from the PS-B shows 62,251 Therms.  In your .inp line 14545 you define your fuel meter units as 89,000 BTU/Therm – so 62,251 Therms is 5,540 MBTU.  Your results are consistent. 
 
  
 

 
  
 
Footprint

Brian Fountain
Associate


 
  
 
From: Equest-users <equest-users-bounces at lists.onebuilding.org>On Behalf Of Ahmad Fraij via Equest-users
Sent: Thursday, November 11, 2021 1:36 AM
To: Fraij via Equest-users <equest-users at lists.onebuilding.org>
Subject: [Equest-users] Gas Consumption Difference
 
  
 
CAUTION: EXTERNAL SENDER 
 
Hello Guys,
 
  
 
When I run the simulation of the attached school building, I get the gas consumption results with very big scale (1,000,000,000 Btu) while the gas consumption results are much smaller than that as per the attached "Results File". Further, the results in the attached file is different from what I get in PS-B report as shown below. Does anybody encountered similar thing and please advise how to fix it. I also attached to this email the .pd2 and .inp files. Thanking you in advance for the help.
 
  
 

 
Regards
 
  
 
Ahmad
   
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20211111/3ce806ec/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 7144 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20211111/3ce806ec/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 33381 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20211111/3ce806ec/attachment-0007.png>


More information about the Equest-users mailing list