[Equest-users] Gas Consumption Difference

Brian Fountain Brian.Fountain at sa-footprint.com
Thu Nov 11 02:30:32 PST 2021


Your results are shown as 5.54 x 109 BTU or 5,540 MBTU in the .pdf.  The capture from the PS-B shows 62,251 Therms.  In your .inp line 14545 you define your fuel meter units as 89,000 BTU/Therm – so 62,251 Therms is 5,540 MBTU.  Your results are consistent.

[cid:image002.png at 01D7D6BD.42FB7DE0]

Footprint

Brian Fountain
Associate


From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Ahmad Fraij via Equest-users
Sent: Thursday, November 11, 2021 1:36 AM
To: Fraij via Equest-users <equest-users at lists.onebuilding.org>
Subject: [Equest-users] Gas Consumption Difference

CAUTION: EXTERNAL SENDER
Hello Guys,

When I run the simulation of the attached school building, I get the gas consumption results with very big scale (1,000,000,000 Btu) while the gas consumption results are much smaller than that as per the attached "Results File". Further, the results in the attached file is different from what I get in PS-B report as shown below. Does anybody encountered similar thing and please advise how to fix it. I also attached to this email the .pd2 and .inp files. Thanking you in advance for the help.

[Inline image]
Regards

Ahmad
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20211111/8e71e298/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 33381 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20211111/8e71e298/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 7144 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20211111/8e71e298/attachment-0007.png>


More information about the Equest-users mailing list