[Equest-users] Baseline Service water heating
Nicholas Caton
Nicholas.Caton at se.com
Thu Sep 10 11:08:21 PDT 2020
I agree with the guidance/discussion so far (the Standard is relatively clear in prescribing natural gas, or possibly propane if your AHJ/rating-authority accepts), but I’m left a little unsatiated… Can we take a step back and discuss the Standard a little further?
What could be the basis or rationale for 90.1 deciding to diverge from “baseline should match the existing system, as applicable?” Prescribing a service water heating system on the basis of building occupancy certainly adds extra nuance/complexity, and demonstrably can result in existing/real service hot water baseline systems being represented with potentially unrealistic system/fuel types.
I trust the 90.1 committee made this change with deliberation, and fully expect I am missing some part of the bigger picture, but would like to be educated if anyone has a sense of why we’re moving in this particular direction.
Thanks!
~Nick
For mutual reference, In 90.1-2010 Table G3.1 reads as follows:
[cid:image002.png at 01D6869E.F908B320]
With 90.1-2013, the same passage (highlighted) was revised as follows:
[cid:image005.png at 01D6869E.48012E40]
[cid:image007.png at 01D6869E.48012E40]
And here is the referenced table:
[cid:image008.png at 01D686A1.9B174B20]
[cid:image006.jpg at 01D68773.5A941010]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Energy and Sustainability Services
Energy Performance Contracting
D
M
E
913 . 564 . 6361
785 . 410 . 3317
nicholas.caton at se.com<mailto:nicholas.caton at se.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
[cid:image003.png at 01D6869B.3CE5BBF0]
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Chapin, Alex N via Equest-users
Sent: Tuesday, September 8, 2020 5:20 AM
To: Rushi Quest <rushiquest at gmail.com>; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Baseline Service water heating
[External email: Use caution with links and attachments]
________________________________
Hi Rushi,
The exception to Table G3.1.11.j (Baseline) states that you should use propane at the fuel source in the baseline when natural gas is not available at your site. In that case, it’s up to you to find a price for propane in your area or use EIA’s propane prices website like https://www.eia.gov/dnav/pet/pet_pri_wfr_dcus_nus_w.htm.
Alex Chapin EIT, BEMP, LEED AP BD+C, O+M
Energy Engineer | Mason & Hanger
A Day & Zimmermann Company
O 804.521.7072
4880 Sadler Road, Suite 300 | Glen Allen, VA 23060
masonandhanger.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.masonandhanger.com%2F&data=02%7C01%7CNicholas.Caton%40se.com%7C9c1bbf019e014ece8d0908d853e0bd9f%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637351572010156163&sdata=HL9l2x%2FZfz2GODC1cXq%2Bm4NqEuCbr7y5cCV%2FSjf5sEg%3D&reserved=0>
An ISO 9001 Certified Company<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.masonandhanger.com%2Fabout%2Fiso&data=02%7C01%7CNicholas.Caton%40se.com%7C9c1bbf019e014ece8d0908d853e0bd9f%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637351572010156163&sdata=onGbHvlNAiwLe5mK%2FiZmT4qui95zq4onFdmY4f30%2BeY%3D&reserved=0>
Building a More Secure World ®
CAUTION - THIS EMAIL MAY CONTAIN CONFIDENTIAL INFORMATION
This electronic mail transmission and any accompanying documents may contain information belonging to the sender, which may be proprietary, confidential, and/or otherwise subject to restrictions on disclosure beyond the intended recipient. This information is intended only for the use of the individual or entity to whom this electronic mail transmission was sent as indicated above. If you are not the intended recipient, any disclosure, copying, distribution, or action taken in reliance on the contents of the information contained in this transmission is strictly prohibited. If you have received this transmission in error, please call 1-703-955-5702 and delete this transmission. Thank you.
From: Rushi Quest [mailto:rushiquest at gmail.com]
Sent: Monday, September 7, 2020 3:30 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Baseline Service water heating
Dear E-questers,
I am working on a hospital building project which uses existing heat pump at site for service water heating.
The issue is arising in modeling baseline hot water system, which as per ASHRAE 90.1-2013 Table G3.1.1-2 is specified as gas storage water heater for hospital building type. The gas utility rates will not be available for the project since no gas heating system is used at site.
I want to confirm whether identical system as proposed case can be considered in baseline model as the energy cost savings will need to be compared with existing heat pump at site.
Thanks in advance.
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200910/685d181a/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 8477 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200910/685d181a/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 271680 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200910/685d181a/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 129110 bytes
Desc: image007.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200910/685d181a/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 248782 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200910/685d181a/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.png
Type: image/png
Size: 156498 bytes
Desc: image008.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200910/685d181a/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.jpg
Type: image/jpeg
Size: 1793 bytes
Desc: image006.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200910/685d181a/attachment.jpg>
More information about the Equest-users
mailing list