[Equest-users] Baseline Service water heating
Chapin, Alex N
Alex.Chapin at masonandhanger.com
Tue Sep 8 03:19:45 PDT 2020
Hi Rushi,
The exception to Table G3.1.11.j (Baseline) states that you should use propane at the fuel source in the baseline when natural gas is not available at your site. In that case, it’s up to you to find a price for propane in your area or use EIA’s propane prices website like https://www.eia.gov/dnav/pet/pet_pri_wfr_dcus_nus_w.htm.
Alex Chapin EIT, BEMP, LEED AP BD+C, O+M
Energy Engineer | Mason & Hanger
A Day & Zimmermann Company
O 804.521.7072
4880 Sadler Road, Suite 300 | Glen Allen, VA 23060
masonandhanger.com<http://www.masonandhanger.com/>
An ISO 9001 Certified Company<https://www.masonandhanger.com/about/iso>
Building a More Secure World ®
CAUTION - THIS EMAIL MAY CONTAIN CONFIDENTIAL INFORMATION
This electronic mail transmission and any accompanying documents may contain information belonging to the sender, which may be proprietary, confidential, and/or otherwise subject to restrictions on disclosure beyond the intended recipient. This information is intended only for the use of the individual or entity to whom this electronic mail transmission was sent as indicated above. If you are not the intended recipient, any disclosure, copying, distribution, or action taken in reliance on the contents of the information contained in this transmission is strictly prohibited. If you have received this transmission in error, please call 1-703-955-5702 and delete this transmission. Thank you.
From: Rushi Quest [mailto:rushiquest at gmail.com]
Sent: Monday, September 7, 2020 3:30 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Baseline Service water heating
Dear E-questers,
I am working on a hospital building project which uses existing heat pump at site for service water heating.
The issue is arising in modeling baseline hot water system, which as per ASHRAE 90.1-2013 Table G3.1.1-2 is specified as gas storage water heater for hospital building type. The gas utility rates will not be available for the project since no gas heating system is used at site.
I want to confirm whether identical system as proposed case can be considered in baseline model as the energy cost savings will need to be compared with existing heat pump at site.
Thanks in advance.