[Equest-users] Temperature Control of Zone Level Exhaust

Nicholas Caton Nicholas.Caton at se.com
Sun Nov 29 22:07:58 PST 2020


My mind immediately jumped to Brian’s second solution.

It’s helpful context while game planning your approach to consider that if you schedule a fan to operate using your own custom schedule, then you have some flexibility to specify the makeup source as either “raw” OA  (EXHAUST-SOURCE = INFILTRATION or BALANCED-INFIL), or conditioned air via the associated SYSTEM (EXHAUST SOURCE = AIR-HANDLER).  With the latter option, you can achieve “getting the load onto the system” in a sort of reverse fashion, if that is a concern.

To “spoon feed” an operating schedule via EMIT, utilize the custom hourly reports feature to track and export the interior/exterior temperature of interest.  That 8760 column can then be “logic ’ed” in Excel to determine a binary operating schedule, which can then be pasted into EMIT to generate an INP snippet ready for import.

A shortcoming for this workaround however is that you can’t totally capture the dynamic interactions between an exhaust fan and AC system both cycling/operating based on a common space temperature and properties like space thermal mass which affect how quickly (or if at all) the space can return to an acceptable thermal state with the exhaust and/or system doing its thing.    You could resolve this by doing the custom hourly thing a few times over to see if and how your exhaust operating schedule may change in reaction to the contributions of another conditioning system… until you reach a state of relative “convergence” where the operating hours aren’t changing much between each round of edits… but then like with many things you will want to consider your time-value for model development and whether you are accomplishing improved levels of accuracy on something important or not in the scheme of things…

Kind regards,

~Nick
[cid:image002.jpg at 01D6C727.F964E7C0]
Nick Caton, P.E. (US), BEMP
ニック ケートン, P.E. (US), BEMP
Senior Energy Engineer
Energy Manager, Yokota Airbase
ESS - Energy & Sustainability Services
M JP
M US
Email
+81 . 070 . 3366 . 3317
+1   . 785 .  410  . 3317
nicholas.caton at se.com<mailto:nicholas.caton at se.com>
シニアエネルギーエンジニア
横田基地エネルギーマネージャー
ESS - エナジー持続可能性サービス

[cid:image003.png at 01D6C727.F964E7C0]
[cid:image004.png at 01D6C727.F964E7C0]
 [cid:image002.jpg at 01D6C727.F964E7C0]


From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Brian Fountain via Equest-users
Sent: Saturday, November 28, 2020 3:41 AM
To: Omer Moltay <omoltay at mimtarch.com>
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Temperature Control of Zone Level Exhaust


[External email: Use caution with links and attachments]

________________________________


Omer,

I have not found a way to operate an EF based on OAT directly.  We have modelled spaces, such as electrical rooms, that are only conditioned by an exhaust fan on a thermostat with a relief intake louver.  We used a 100% OA supply fan – usually a PSZ system with cooling set to 1 BTU/hr to prevent autosizing.  The fan input power matched the exhaust fan and it is controlled either to ‘intermittent’ operation or it is set always to unoccupied with its night cycle control set to ‘cycle on any’.

This suggestion would be less helpful if you have other systems serving the same space.  In that case I guess you’d create a custom schedule for the exhaust fan.  I still like RMI’s EMIT spreadsheet for creating custom eQUEST schedules.

Cheers,

Brian

Footprint
From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Omer Moltay via Equest-users
Sent: November 27, 2020 1:04 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Temperature Control of Zone Level Exhaust

CAUTION: EXTERNAL SENDER

Dear All,

Is it possible to model zonal exhaust schedules in eQuest to turn on/off based on indoor temperature of the zone?

Thanks in advance for the replies,

Ömer Moltay, LEED AP BD+C, ASHRAE BEMP, ASHRAE CPMP
Mimta EcoYapi, LEED Proven Provider
Hekimsuyu Cad. 559. Sk.
No:39 34255 Kucukkoy Istanbul Turkey
Tel: 90-212-617-2296
Fax: 90-212-617-2297
Mobile: 90-533-957-1394
www.eco-yapi.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.eco-yapi.com%2F&data=04%7C01%7CNicholas.Caton%40se.com%7C198a8361265f4afd955908d893040fec%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637420992944301550%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=aPQiAnSV0DB1H4QAPWV2o5FktWeqbR3zqSI9RYC7XFI%3D&reserved=0>
www.buildingenergymodels.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.buildingenergymodels.com%2F&data=04%7C01%7CNicholas.Caton%40se.com%7C198a8361265f4afd955908d893040fec%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637420992944301550%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&sdata=h%2FOngZVBebl1HR0C%2BgbTUi8CMIHTKiZfeQSCMEtyD7k%3D&reserved=0>

[imap://omoltay%40mimtarch%2Ecom@secureams44.sgcpanel.com:993/fetch%3EUID%3E.INBOX%3E106681?header=quotebody&part=1.2&filename=image001.png]



______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201130/13fbcc60/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1794 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201130/13fbcc60/attachment-0003.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 1947 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201130/13fbcc60/attachment-0009.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 6510 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201130/13fbcc60/attachment-0010.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 44049 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201130/13fbcc60/attachment-0011.png>


More information about the Equest-users mailing list