[Equest-users] Water cooled VRF with DOAS
Nicholas Caton
Nicholas.Caton at se.com
Mon Jun 15 13:47:58 PDT 2020
Bryan:
I’ve poked around a bit over the last week. Have a couple questions/prompts questions that may help you directly, or help others in advising you.
Can you assert:
* What are your expectations for what CW supply temps (seen @ each VRF for heat transfer) should look like as a function of season / conditions /etc? You might in parallel want to look hard at what’s simulated in the moment.
* Please contrast the (intended) CW supply temps against the conditions used to assert the heating/cooling capacities entered for each VRF
I’ll also observe, as this may be tied to some of the unmet hours you’re tackling in the moment – you may have a few issues in your implementation of the dummy zone approach/workaround:
* Your VRF systems (as named) aren’t consistently using the OA-FROM-SYSTEM input, as may be intended
* Be mindful the DOAS system and its dummy zone are “in a bubble” with respect to the conditioning loads for the ventilation air. If there is any humidity control to occur at the DOAS, you might struggle with such a high drybulb limit for economizer operations. On the flip side, if it’s expected the DOAS will pass overly-humid air to the distributed cooling coils, I don’t think this workaround in doe2.2 will do the job of transmitting that latent load for you – it may be a manual process of defining some small process space saunas or similar ;-).
For all: These nuances in VRF/DOAS implementation are part of the reason I really try to stress with friends to utilize the newer doe2.3 feature sets for VRF and DOAS when feasible. In Bryan’s case, I don’t think waterside VRF has made the transition just yet… but I bring this up to make clear I am not endorsing doe2.2-era workarounds for DOAS/VRF where they are avoidable in this day and age.
~Nick
[cid:image004.jpg at 01D6432C.55CFEBC0]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Energy and Sustainability Services
Energy Performance Contracting
D
M
E
913 . 564 . 6361
785 . 410 . 3317
nicholas.caton at se.com<mailto:nicholas.caton at se.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
[cid:image003.png at 01D6431D.C0C707B0]
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Bryan Papaj via Equest-users
Sent: Tuesday, June 2, 2020 9:02 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Water cooled VRF with DOAS
[External email: Use caution with links and attachments]
________________________________
Hello,
Hello,
I have a water-cooled VRF system with a DOAS. I modeled this as each individual zone getting its own individual PSZ and followed the eQuest modeling tutorial from Mitsubishi. The DOAS was modeled with a dummy zone and feeds each VRF zone with the OA-From DOAS. The problem that I am facing is that when I am simulating I have many unmet hours for the VRF zones and when I review the SS-A System Loads Summary Report I see that there is no cooling or heating energy. Has anyone experienced this before and if so how can I load the VRF system? Also, is there a way to see the individual zone heating or cooling contributions from the DOAS.
I have attached my pd2 and inp eQuest files.
Regards,
--
Bryan Papaj
Energy Engineer
C. J. Brown Energy, P.C.
4245 Union Rd, Suite 204
Buffalo, NY 14225
Phone: (716) 565-9190 Fax: (716) 633-5598
Email: bmp at cjbrownenergy.com<mailto:bmp at cjbrownenergy.com>
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200615/e05788cd/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 8477 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200615/e05788cd/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 1794 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200615/e05788cd/attachment.jpg>
More information about the Equest-users
mailing list