[Equest-users] Assign 2 systems to the same zone

Nicholas Caton Nicholas.Caton at se.com
Tue Jul 7 05:49:26 PDT 2020


Hi Tanya!

There is a long-standing limitation with doe2/eQuest in not permitting more than one system per zone, however in recent years, this rule has been relaxed a bit.

If you treat your AHU as a DOAS system (responsible for delivering ventilation air), then you can have a DOAS + another system technically servicing the same zone.  This does require building your model using the doe2.3 engine.

If a DOAS circumstantially will not work however, and you wish to model 2 or more systems servicing the same zone, there remains a couple long-standing “workarounds” I’ve seen promoted in this community:

  1.  The targeted zone can be split into 2 or more air-wall sharing spaces, geometrically considering where the thermostats for the various systems actually lie and (if skin loads are in play) which system is intended to handle specific space loads. Changing up model geometries is totally possible, but can be a more involved proposition post-wizards.  I recommend newer energy modelers to move back to wizards if they aren’t too far past the line of detailed mode edits.
  2.  The presence of a second system can sometimes be approximated through cleverly tweaking one system and adding zonal baseboards or zonal heating/cooling coils, if applicable.  This can require sacrificing some degree of capacity for independent system operation, but in some cases is a totally fair representation in terms of model accuracy.
  3.  I’ve seen a couple cases where the modeler chose to duplicate the associated space/zone, assign its internal loads (like lights/ plug loads) to “ghost” meters (to prevent double counting those energies), then assign a second system to the duplicated zone.  This can be problematic relative to the other options presented, in that you’re missing any opportunity to capture the interactivity between the systems.  In some cases however, you might not want to model interactivity… just consider that one systems’ controlling thermostat may be affected by space heating/conditioning performed “by others.”

I hope this is helpful!

~Nick

[cid:image001.jpg at 01D65433.20CDC5B0]
Nick Caton, P.E., BEMP
  Senior Energy Engineer
  Energy and Sustainability Services
  Energy Performance Contracting
D
M
E

913 . 564 . 6361
785 . 410 . 3317
nicholas.caton at se.com<mailto:nicholas.caton at se.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219

[cid:image002.png at 01D65433.20CDC5B0]


From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Tanya Soji via Equest-users
Sent: Tuesday, July 7, 2020 6:30 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Assign 2 systems to the same zone


[External email: Use caution with links and attachments]

________________________________


Hi everyone,

I just wanted a small clarification on the Air-side HVAC systems.

How does  eQuest go about assigning two different HVAC systems (AHUs & Package units in my case) to the same zone??

It does not let me add the same zones to the second system (Package units).

Regards,

Tanya

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
This e-mail is from Eurostar Group. is intended solely for the person to whom it has been addressed. It should not be used by anyone else. It may contain confidential and/or legally privileged information. If you are not the intended recipient, you are notified that any use, distribution, transmission, printing, copying, dissemination or any action in reliance on it is strictly prohibited. If you have received this email erroneously, please delete this message and notify the sender.
The recipient acknowledges that Eurostar Group /subsidiaries/ associated companies, are unable to exercise control or ensure or guarantee the integrity of/over the contents of the information contained in e-mail transmissions and further acknowledges that any views expressed in this message are those of the individual sender and no binding nature of the message shall be implied or assumed unless the sender does so expressly with due authority of Eurostar Group.  If the recipient thinks that any part of this email transgresses any law of the land, he/she I shall immediately alert Eurostar Group, by mailing their specific concern on marketing at eurostargroup.com<mailto:compliance at eurostargroup.com> Needless to reiterate that Consequently,  Eurostar does not take any liability whatsoever, for any such transgressions.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200707/272099f9/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1794 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200707/272099f9/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200707/272099f9/attachment-0002.png>


More information about the Equest-users mailing list