[Equest-users] Modeling in ASHRAE 90.1 2016
Javed Iqbal
eee.javed at gmail.com
Tue Oct 15 22:48:22 PDT 2019
Hello Matt,
- ASHRAE 90.1-2016, section G1.2.1 explicitly says that ' *The interior
lighting power shall not exceed the interior lighting power
allowance determined using either Tables G3.7 or G3.8 and the
methodology **described
in Sections 9.5.1 and 9.6.1'*. So it seems you need to refer G3.7 or G3.8
for LPD values and* Methodology* should be as per 9.5.1 and 9.6.1
- Table G3.1 5(a) says '*All components of the building envelope in the
proposed design shall be modeled as shown on architectural drawings or as
built for existing building envelopes*' with some exceptions but none
restricts proposed values.
I haven't used 90.1-2016 to a great extent but standard seems quite
straight forward with some changes in formatting (tables, references etc.)
compared to previous versions. I stand corrected if missed out anything
important.
hope this is helpful.
regards,
On Wed, Oct 16, 2019 at 7:54 AM Matthew S. Garlick via Equest-users <
equest-users at lists.onebuilding.org> wrote:
> Hi all,
>
>
>
> This is my first project using ASHRAE 90.1 2016 and I’m finding some odd
> instructions in Appendix G.
>
>
>
> A couple examples-
>
> - Table G3.1 says that the baseline case is to use table G3.7 to
> define space by space LPD, but the proposed has to comply with section
> 9.1.3. There’s a big difference between maximum allowed LPD between the two
> tables, for example G3.7 calls for open Office areas at 1.1 W/sf but table
> 9.6.1 says 0.81 W/sf.
> - Baseline Wall insulation for climate zone 5b, per table G3.1 and
> G3.4-5 is to be simulated at a U value of 0.084. The proposed case must be
> under 0.055 per table 5.5-5.
>
>
>
> Appendix G now has tables for envelope properties, equipment efficiencies
> and lighting power densities which all conflict with what we’re used to
> finding in sections 5, 6 and 9 in previous iterations of the standard.
> Reading table G3.1 it seems clear that they want us to use the appendix G
> tables to define the baseline and not the tables in the main sections, but
> this makes no sense to me.
>
>
>
> I feel like I’m taking crazy pills…can anyone shine some light on this?
>
>
>
>
>
> [image: TBCx]
>
> *Matt Garlick, CxA, CEM, BEMP*
> Building Efficiency Engineer | TBCx
>
> E-mail: msg at tbcxinc.com
> Mobile: 801-907-5654
> Direct: 801-401-8456
>
> 324 S. State Street, Suite 400
> Salt Lake City, UT 84111
> www.tbcxinc.com <http://tbcxinc.com/>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
--
Javed Iqbal, LEED AP, CEA
Sr. Energy Analyst